Is it possible to use (Powerchute Personal Edition Software) on my APC Smart-UPS C 1500VA 230V (SMC1500I)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Is it possible to use (Powerchute Personal Edition Software) on my APC Smart-UPS C 1500VA 230V (SMC1500I)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
143
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:42 PM . Last Modified: β€Ž2024-03-14 04:06 AM

0 Likes
10
3309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:42 PM . Last Modified: β€Ž2024-03-14 04:06 AM

Is it possible to use (Powerchute Personal Edition Software) on my APC Smart-UPS C 1500VA 230V (SMC1500I)

Hi

Is it possible to use (Powerchute Personal Edition Software) on my APC Smart-UPS C 1500VA 230V (SMC1500I)

thanks

Jonathan

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • edition
  • personal
  • PowerChute
  • software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:42 PM . Last Modified: β€Ž2024-03-14 04:06 AM

0 Likes
0
3310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:42 PM . Last Modified: β€Ž2024-03-14 04:06 AM

Jim,

You only need to install the Agent and yes. Business Edition will show you charge, allow for self-test and update battery info.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:42 PM . Last Modified: β€Ž2024-03-14 04:06 AM

0 Likes
0
3310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:42 PM . Last Modified: β€Ž2024-03-14 04:06 AM

Jonathan,

PowerChute Personal Edition is designed to work with Back-UPS not Smart-UPS. If you are looking for alternative software to us with your SMC and Windows 7 you should look at APCUPSD.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:42 PM . Last Modified: β€Ž2024-03-14 04:06 AM

0 Likes
0
3310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:42 PM . Last Modified: β€Ž2024-03-14 04:06 AM

This is too bad. I would think you'd allow the much easier-to-use personal edition with any product....

So. Do I have to install Agent, Server, and Console for a single computer setup? 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:42 PM . Last Modified: β€Ž2024-03-14 04:06 AM

0 Likes
0
3310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:42 PM . Last Modified: β€Ž2024-03-14 04:06 AM

Also, is there any way to see the % charged, and to force a test, or to register a new battery date in the Bus. Edition?  Thanks!

Jim

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:42 PM . Last Modified: β€Ž2024-03-14 04:06 AM

0 Likes
0
3311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:42 PM . Last Modified: β€Ž2024-03-14 04:06 AM

Jim,

You only need to install the Agent and yes. Business Edition will show you charge, allow for self-test and update battery info.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:43 PM . Last Modified: β€Ž2024-03-14 04:06 AM

0 Likes
0
3310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:43 PM . Last Modified: β€Ž2024-03-14 04:06 AM

Only web based?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:43 PM . Last Modified: β€Ž2024-03-14 04:06 AM

0 Likes
0
3310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:43 PM . Last Modified: β€Ž2024-03-14 04:06 AM

Powerchute Business Edition is far more complicated for my needs. I only purchased the Smart UPS 1000/1500VA because of the wattage and the fact it is pure sine wave output on battery. How can I get a simple interface like Powerchute Personal Edition? The Personal Edition is not compatible with my Smart UPS. Please help!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:43 PM . Last Modified: β€Ž2024-03-14 04:06 AM

0 Likes
0
3310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:43 PM . Last Modified: β€Ž2024-03-14 04:06 AM

You can use APCUPSD. It is freeware available at www.apcupsd.com You have to install their USB driver and edit the configuration file but once that is done the interface is simpler to navigate.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:43 PM . Last Modified: β€Ž2024-03-14 04:06 AM

0 Likes
0
3310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:43 PM . Last Modified: β€Ž2024-03-14 04:06 AM

I wish I had known that personal edition does not work on the SMX1500. Why did APC even include that software? Was it because the Business Edition work? 😞

  • Tags:
  • chute
  • power
  • smx1500
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:43 PM . Last Modified: β€Ž2024-03-14 04:06 AM

0 Likes
0
3310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:43 PM . Last Modified: β€Ž2024-03-14 04:06 AM

What about the network shutdown that came with the SMX1500? Does that not work, too? I'll delete the personal edition and see what happens when Iinstall the apcupd "thingie". πŸ™‚

  • Tags:
  • network
  • shutdown
  • smx
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:43 PM . Last Modified: β€Ž2024-03-14 04:06 AM

0 Likes
0
3310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:43 PM . Last Modified: β€Ž2024-03-14 04:06 AM

Hi,

If your SMX1500 has a network management card install and it is on your network then you can install PowerChute Network Shutdown on to computer assuming it is running a compatible OS (see compatibility chart). PowerChute Network Shutdown will communicate with the NMC / UPS over your network so you will not need to connect a serial (RJ50 - 9 pin Serial) or USB cables between the computer and UPS. You should be sure that any network equipment that is between the NMC and computer are also on a UPS as well to allow communicates between the NMC and computer in the event of a power lose. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore