Hi everyone,
I am having trouble getting this AP9617 card to see the UPS, I have flashed it successfully with fw 3.7.2 but there's no UPS tab available.
I am wondering if it's a compatibility issue and what nmc card is recommended for this unit
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:34 AM . Last Modified: 2024-03-05 12:35 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:34 AM . Last Modified: 2024-03-05 12:35 AM
Thank you for the information JMT. We will purchase the correct card for this unit.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:34 AM . Last Modified: 2024-03-05 12:35 AM
Hi,
The AP9617 card is not compatible with the SMT1500. This card is now obsolete and is compatible with older Smart-UPS units.
The AP9630 and AP9631 are the current cards that are recommended and supported by that UPS.
http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=AP9630
http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=AP9631
Regards
JMT
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:34 AM . Last Modified: 2024-03-05 12:35 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:34 AM . Last Modified: 2024-03-05 12:35 AM
Thank you for the information JMT. We will purchase the correct card for this unit.