Input Phase Selector switch

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Input Phase Selector switch
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
dario_ramos_apc
Lieutenant JG dario_ramos_apc
Lieutenant JG

Posted: ‎2021-06-30 02:12 AM . Last Modified: ‎2024-03-10 11:58 PM

0 Likes
5
1746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:12 AM . Last Modified: ‎2024-03-10 11:58 PM

Input Phase Selector switch

Hi all
Please let me know what happens if I put the Input Phase Selector Switch not in accordance with the power feeding:
- Connect the UPS to a three phase mains and put the switch in "1"
- Connect the UPS in single phase and put the switch in "3"
Can the UPS become damaged because of this mismatch?
Please consider SURT10000XLI UPS.

Thanks in advance

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • apc
  • hardware
  • power
  • smart-ups
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:13 AM . Last Modified: ‎2024-03-10 11:57 PM

0 Likes
0
1746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:13 AM . Last Modified: ‎2024-03-10 11:57 PM

Hi,

I dont have any experience with this issue.

1. But as my knowleage, the switch selection in "1 "will make a solid connect between 3phase input. You will got the short - circuit in case apply the 3 phase to this selection.

Why ?

Rectifier only provide convert from AC to DC.

The IGBT (or SCR in each phase is sized ~ 10kVA/3). in 3:1 mode, it's ok
In the 1:1 mode, the L1 can't support enough capacity so it's will make a solid 3 phase. L1, L2, L3. (The bypass only take from L1).

2. If you put the single phase to but select 3 phase. It's won't have any issue (this is site wiring failure alarm, or make the Input outside of tolerat - run battery).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
dario_ramos_apc
Lieutenant JG dario_ramos_apc
Lieutenant JG

Posted: ‎2021-06-30 02:12 AM . Last Modified: ‎2024-03-10 11:58 PM

0 Likes
0
1746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:12 AM . Last Modified: ‎2024-03-10 11:58 PM

Hi

Thanks for your post but you are wrong.

Your speech assumes that the "input selector phase switch" is a power one and it is not. It is a signal switch, and acts to the control like a setup parameter. It has influence on the UPS behavior and, I think, on the way control modulates input switching when supplying the internal inverter from AC mains.

The UPS doesn't have a controlled switch - IGBT module - per phase. Instead it has a bridge rectifier per phase (two bridges in parallel on phase L1 to support 1:1 running). IGBT modules are assembled after input rectification.

Reply

Link copied. Please paste this link to share this article on your social media post.

dario_ramos_apc
Lieutenant JG dario_ramos_apc
Lieutenant JG

Posted: ‎2021-06-30 02:12 AM . Last Modified: ‎2024-03-10 11:58 PM

0 Likes
0
1746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:12 AM . Last Modified: ‎2024-03-10 11:58 PM

Definitely no one knows something about this?

Reply

Link copied. Please paste this link to share this article on your social media post.

dario_ramos_apc
Lieutenant JG dario_ramos_apc
Lieutenant JG

Posted: ‎2021-06-30 02:12 AM . Last Modified: ‎2024-03-10 11:58 PM

0 Likes
0
1746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:12 AM . Last Modified: ‎2024-03-10 11:58 PM

Hi all
Are you in vacations

Reply

Link copied. Please paste this link to share this article on your social media post.

dario_ramos_apc
Lieutenant JG dario_ramos_apc
Lieutenant JG

Posted: ‎2021-06-30 02:12 AM . Last Modified: ‎2024-03-10 11:57 PM

0 Likes
0
1746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:12 AM . Last Modified: ‎2024-03-10 11:57 PM

Hi there

Pleeeeeeease can you leave here any support to my inquiry?

I have one SURT10000XLI that was connected to a three phase system with the phase selector switch in the position "1".
The input/battery converter - PFC or DC/DC from batteries - became damaged. One IGBT module was broken.

I would like to know if those things - switch position and converter damage - can be correlated.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:13 AM . Last Modified: ‎2024-03-10 11:57 PM

0 Likes
0
1747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:13 AM . Last Modified: ‎2024-03-10 11:57 PM

Hi,

I dont have any experience with this issue.

1. But as my knowleage, the switch selection in "1 "will make a solid connect between 3phase input. You will got the short - circuit in case apply the 3 phase to this selection.

Why ?

Rectifier only provide convert from AC to DC.

The IGBT (or SCR in each phase is sized ~ 10kVA/3). in 3:1 mode, it's ok
In the 1:1 mode, the L1 can't support enough capacity so it's will make a solid 3 phase. L1, L2, L3. (The bypass only take from L1).

2. If you put the single phase to but select 3 phase. It's won't have any issue (this is site wiring failure alarm, or make the Input outside of tolerat - run battery).

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore