Input Frequency and Voltage Alerts

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Input Frequency and Voltage Alerts
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
pdixon
pdixon
Cadet

Posted: ‎2025-02-18 06:05 AM . Last Modified: ‎2025-02-18 06:12 AM

0 Likes
3
212
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-18 06:05 AM . Last Modified: ‎2025-02-18 06:12 AM

Input Frequency and Voltage Alerts

My company has Distilleries in rural locations, and we have power that is apparently not very stable. We have at least 20+ APC UPS's at each site, as well as 300+ in offices around the world. We see constant alerts for input voltage and frequency issues. The power does fluctuate a little, but not to the point is has caused issues with anything other than the UPS's. Our electricians say that everything is within the acceptable range. We had to disable email alerts and forward the alerts to a log server, and get daily reports. We were getting so many email alerts a day our email provider accused of a denial of service attack. We selected APC UPS's because we wanted a reliable backup for power loss. I was under the impression that a UPS's job was to take fluctuation voltage and maintain consistent voltage. The alerts we se below are listed below as well as the alerts from two UPS's from a daily report. The number at the end of the alert summary are the number or alerts in the past 24 hours.

 

UPS: Bypass not in range low voltage.
UPS: Bypass not in range either frequency or voltage.
UPS: Bypass not in range distorted waveform.

 

UPS-WRD-Distillery-1 UPS: Bypass not in range either frequency or voltage. 410
UPS-WRD-Distillery-1 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 410
UPS-WRD-Scalehouse-1 UPS: Bypass not in range either frequency or voltage. 629
UPS-WRD-Scalehouse-1 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 629

 

Finally my question, is there a way to adjust the voltage\frequency range to prevent these alerts. I have tried to adjust the Power Setting Configuration on the UPS with no luck. We acknowledge that the fluctuation may affect bypass mode, but all of the alerts cause serious alerts to be missed because of all of the noise. Any ideas?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Janeway Teken
Janeway

Posted: ‎2025-02-19 06:53 AM

0 Likes
2
191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-19 06:53 AM

Since you have provided no specific information as to the actual APC UPS Model. My reply will be over generalized to cover as many possibilities as to a solution vs band aid.

 

The limited information you provided indicates the system is operating as designed. Because the system sees dirty power whether voltage variation, frequency drift, THD.

 

I have yet to meet any electrician worth their salt when asked to validate the input power is considered *Clean*! 🤦‍♂️

 

Your electrician has simply recited the exact same answer as the other 99999999 so called professionals before him. 🤢

 

If he actually did his job it would have taken no less than a week to come back to you with recorded factual data. Dollars to donuts he took a cheap meter and stuck it into an outlet and measured and said good?!? 🤣

 

Ask him to provide you the data from his Fluke Power Quality Meter. The short & long term measurements are taken at the service entrance, service panel, and target location of the end devices.

 

Regardless, in larger enterprise systems you have the ability select power quality and transfer voltage. Both of these settings determine if and when the system will use the AVR circuit vs the inverter battery mode.

 

If the system is defined to use battery only mode this of course impacts the battery service life. Thus, long term costs for battery replacements! ☝️

 

Your first step is to determine if all the attached loads are fine to accept *Dirty Power*. If so adjust the system to the widest margin from normal to low.

 

Adjust the input transfer voltage for both upper / lower to the highest setting. Doing so means the system will be forced to accept higher / lower input voltages.

 

Higher end models will allow you to adjust the allowable frequency drift. Lastly, none of the settings noted up above will negate the system from acting if and when there is a surge event or fast transient.

 

Questions Ask . . . 

Reply

Link copied. Please paste this link to share this article on your social media post.

pdixon
pdixon
Cadet

Posted: ‎2025-02-20 06:25 AM

In response to Teken
0 Likes
1
171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-20 06:25 AM

Forgive me for my lack of detail, and thank you for your response. The UPS in my example is a Smart-UPS SRT 1500, and is used to power Cisco network equipment. I agree with your statement regarding electricians, but they acknowledge voltage fluctuation. If it were one or two having that issue then I would suspect a local issue, but this is happening to all of the newer APC models (Smart-UPS SRT 1500).  Our older UPS's (APC Smart UPS 1500 and Liebert GXT4) were in the process of replacing have never had alerts for power issues or failed to provide power when needed. I know that the 1500 series is a small UPS with fewer configuration options, and I am not having widespread issues with 300+ UPS's. The location in my example is a bourbon distillery 10 miles away from the nearest four lane road and is surrounded by horse farms. It is a beautiful place but the power will fluctuate and have the occasional outage. The UPS's seen to be the only devices that seem to have issues with the power. I attached a sensor graph of the voltage for the past 30 days. 

My goal is to reduce the amount of alerts, and wanted to ask my peers for recommendations. I 

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Janeway Teken
Janeway

Posted: ‎2025-02-20 08:37 AM

In response to pdixon
0 Likes
0
168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-20 08:37 AM

As stated the system is operating as expected in the default state. You may change both the sensitivity (Power Quality) and transfer voltage on the system to accept the *Dirty Power* if you wish.

 

So long as you have validated all the connected loads are fine with being fed this power. The vast majority of enterprise hardware are wide input voltage and dual frequency.

 

As such they have no problem receiving less than ideal input voltage. Again, you must test and validate if your connected loads are fine receiving the same.

 

Another method is to simply define the email alert to a longer threshold or just turn it off completely. Which obviously negates even being made aware of the problem.

 

You can use one or both methods to address the issue at hand. As stated the UPS is operating as expected and protecting your connected loads and informing you of the same. 

Lastly, my statement about the electrician wasn’t a stab at the fellow. So much as this is the reality of people in this field / industry. We have millions of sites and all of our electricians and engineers are top shelf.

 

But, all of them have been trained to actually use their brain and purpose built tools to provide facts / data. Not an easy out answer of *This is within range / margins* of the POCO! 🤦‍♂️

 

That kind of reply comes from the lazy, unskilled, and untrained so called professional regardless of the field! 👎

 

This is why people who train and work in Power Management exists. They understand all the steps and procedures and use certified equipment to test, monitor, and record the power quality. They take that factual data and present the same to the powers that be.

The outcome depends upon the environment, circumstances, and the persons / companies level of concern.

 

Ultimately, you have a double conversion pure sine wave UPS in place because it provides stable power. As your supply is less than reliable or clean so there’s nothing more to do besides the recommendation outlined above. 🤟

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of