On Surt3000uxi ups when input available and turn on ups indicate system fault and battery bar 3rd and 5 led flashing.
Thanks,
Vijay Mali
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:36 AM . Last Modified: 2024-03-12 03:37 AM
I can only find:
0
0
0
1
1
which indicates a high output voltage (staying over 269V for several AC line cycles) - have you measured the output voltage?
I also can only find this and not the first indicator you gave me:
0
0
1
0
1
(which is Output relay fault)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:36 AM . Last Modified: 2024-03-12 03:37 AM
Dear Sir/Madam
On Surt3000uxi ups when input available and turn on ups indicate system fault and battery bar 3rd and 5 led flashing.
Thanks,
Vijay Mali
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:36 AM . Last Modified: 2024-03-12 03:37 AM
Dear Angela,
I had counting indicates from bottom to top
1
0
1
0
0
or
0
0
0
1
1
When input available and on battery mode.
Regards,
Vijay Mali
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:36 AM . Last Modified: 2024-03-12 03:37 AM
I can only find:
0
0
0
1
1
which indicates a high output voltage (staying over 269V for several AC line cycles) - have you measured the output voltage?
I also can only find this and not the first indicator you gave me:
0
0
1
0
1
(which is Output relay fault)