Incompatible battery pack on Smart-UPS Ultra (SRTL3KRM1UINC)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Incompatible battery pack on Smart-UPS Ultra (SRTL3KRM1UINC)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
AiBE
AiBE
Cadet

Posted: ‎2024-10-04 01:23 AM

0 Likes
3
1023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-04 01:23 AM

Incompatible battery pack on Smart-UPS Ultra (SRTL3KRM1UINC)

Hi.

I got a APC Smart-UPS Ultra (Smart-UPS 3000 in webgui) with the SKU SRTL3KRM1UINC with a batterypack with SKU SRTL50RMBP1U-LI.

After installation the UPS went on without any problems. Then I tried to disconnect the external batterypack, and after reconnecting it the UPS now got an critical alarm present: "UPS: Battery pack 1 is not compatible with this UPS."

Estimated runtime is as if the external battery is connected.

Is the external battery pack really incompatible with my UPS? How to get rid of the critical event?

Model: Smart-UPS 3000
SKU: SRTL3KRM1UINC
Firmware Revision: UPS 01.3 (ID1062)
External Battery SKU: SRTL50RMBP1U-LI

Cheers!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Kirk Teken
Kirk

Posted: ‎2024-10-04 02:45 AM

0 Likes
2
1020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-04 02:45 AM

I would ask you to confirm if the CAN Bus terminator is properly installed on the extended battery pack as outlined in the users manual on page 11.

 

I have appended the user manual for your reference here: 

 

https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=SUO+UM+990-6315A+MN...

 

Lastly, have you tried to reboot the NMC / UPS if the terminator is in place?!?

 

Please do let me know 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

AiBE
AiBE
Cadet

Posted: ‎2024-10-13 11:36 PM

In response to Teken
0 Likes
1
926
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-13 11:36 PM

Yes, the CAN bus terminator is properly installed.
Have also tried to restart the UPS and the networkcard without any result.

Did a shutdown on the UPS, disconnected the external battery, turned on the UPS again. The critical event was now that the external battery was disconnected/missing.

Did then a factory reset of the UPS. The event was now gone. Did a shutdown on the UPS, reconnected the external battery and then turned on the UPS. During the boot something went terrible wrong and something broke loudly and I could smell electrical fire. The display of UPS went red and showed a error message.

Afterwards I hope that it was our APC PDU that broke. Ripped out all the cables from UPS and then booted the UPS on internal batteries, and it started without any messages.

Troubleshooting continues..

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-10-14 04:58 AM

In response to AiBE
0 Likes
0
923
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-14 04:58 AM

Please submit formal service request with APC Technical Support. Engage the EPO on the system. 


Disconnect the unit from AC Mains and stop using the unit. Move the entire system outside in a secure area clear of any combustible materials.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.