InRow Cable Connetions - Why are two Ethernet Cables required?
  • InRow Cable Connetions - Why are two Ethernet Cables required?
Posted: ‎2021-06-28 07:04 AM . Last Modified: ‎2024-03-18 12:55 AM
1340
In setting up an InRow, I discovered that you need to connect an Ethernet cable to the comms card for network capability AND you need to connect all the devices together using the A-link connections so the units will communicate as a group. That is a lot of cable. Can I only connect them using the Comms connection to my network and then tell them which units are in the same group?
Please advise if I can or if not, why? does it have to do with not flooding the network lines with data packets between the units?
J
  • acsc100
  • inrow
  • network_management_card
Sure thing!
J.Smith:
In regards to the various connections on the unit, unfortunately group communication cannot be done via the ethernet connection. This connection is only for communication to the web interface of the device, as well as other forms of network communication such as email or SNMP. The group communication is done via A-link ports, and while they use ethernet connections to make the cabling standard, it is effectively a serial bus, and shares nothing with normal network communication, hence why it is done this way. I apologize for any inconvenience, but if you have any other questions, please feel free to ask. Thank you.
L2SupportServices-Cooling - could you help with this one please? Thanks!
Sure thing!
J.Smith: