Hi,
I'm running a SUA1500 directly connected via USB to a Vista SP1 x64 machine. I'm using PCBE Agent to access the UPS thanks to "i picKed a winna." However, when I click on Data Log -> View Log the time assigned to a given entry is off by 7 hours (e.g., data log entry time shows 07:37:34 when it is 2:37 AM). How do I set the time/timezone so I can correct this?
Thank you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:59 AM . Last Modified: 2024-03-07 10:22 PM
If you can only use 7.0.5 and can't upgrade to 8.0, here is the link for download PCBE 705 patch for Vista:
http://www.apcc.com/tools/download/software_comp.cfm?sw_sku=SFPCBE705vup
fyi, this issue you are seeing was mentioned in 7.0.5 and 8.0 Release Notes. however, I believe this issue should have been fixed in 8.0. Release Notes will be addressed in future version I believe.
Message was edited by: annwang
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:58 AM . Last Modified: 2024-03-07 10:22 PM
when you log into the powerchute agent, click on Help->About Powerchute to find out your agent version number.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:59 AM . Last Modified: 2024-03-07 10:22 PM
Hi,
What's PCBE version? If it is 7.0.5, you need to install PCBE 705 patch for Vista.
Message was edited by: annwang
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:59 AM . Last Modified: 2024-03-07 10:22 PM
How can I tell what version of PCBE I'm running via the Agent? When you refer to this PCBE patch are you referring to the JRE configuration tool? I downloaded this and switched the JRE PCBE was using from 1.42 to 1.6.x and it seemed to solve the problem.
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:59 AM . Last Modified: 2024-03-07 10:22 PM
Looks like I'm running version: 7.0.5.108. Where can I download this patch unless we're talking about the JRE Configuration Tool?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:59 AM . Last Modified: 2024-03-07 10:22 PM
If you can only use 7.0.5 and can't upgrade to 8.0, here is the link for download PCBE 705 patch for Vista:
http://www.apcc.com/tools/download/software_comp.cfm?sw_sku=SFPCBE705vup
fyi, this issue you are seeing was mentioned in 7.0.5 and 8.0 Release Notes. however, I believe this issue should have been fixed in 8.0. Release Notes will be addressed in future version I believe.
Message was edited by: annwang
Link copied. Please paste this link to share this article on your social media post.