How to schedule shutdown/restart the UPS by telnet command line (by using AP9630 Network Management card 2)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How to schedule shutdown/restart the UPS by telnet command line (by using AP9630 Network Management card 2)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:40 AM . Last Modified: ‎2024-03-13 12:44 AM

0 Likes
12
4107
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:40 AM . Last Modified: ‎2024-03-13 12:44 AM

How to schedule shutdown/restart the UPS by telnet command line (by using AP9630 Network Management card 2)

Hi

I would like to schedule a specific time to shutdown the UPS and schedule a specific time to restart the UPS by telnet .  for example I want to schedule to shutdown the ups in 8 hours and restart it in 12 hours.

Thanks a lot for any help!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:41 AM . Last Modified: ‎2024-03-13 12:43 AM

0 Likes
0
4102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:41 AM . Last Modified: ‎2024-03-13 12:43 AM

We bought around 280 pieces of 9630 card (v,5.1.7)  and around 30 piece of 9617 (v.3.6.1 ).  sounds all of them are blue web interface

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:40 AM . Last Modified: ‎2024-03-13 12:44 AM

0 Likes
0
4102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:40 AM . Last Modified: ‎2024-03-13 12:44 AM

Hi Angela,

Could you please give me an example by using CLI to schedule shutdown the UPS and turn the UPS back in 10 hours by using 9630 card? 

Many Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:40 AM . Last Modified: ‎2024-03-13 12:44 AM

0 Likes
0
4102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:40 AM . Last Modified: ‎2024-03-13 12:44 AM

AP9630 is our current platform. AP9617 has been discontinued for about 5 years now...

AP9617 will be easier - it has a menu driven command line interface. You'd need to go to the Device Manger Menu, select your UPS, and within there, you'd be able to Control the UPS and set a sleep time by reviewing the options on the screen.

v5.1.7 on AP9630 you need to look at the commands I mentioned...

Usage: cfgshutdn  -- Configure UPS shutdown parameters

    cfgshutdn [-all] (Show all applicable shutdown parameters for this UPS)

        [-sd <000 | 090 | 180 | 270 | 360 | 450 | 540 | 630>] (Shutdown Delay, in seconds)

        [-lo <02 | 05 | 08 | 11 | 14 | 17 | 20 | 23>] (Low Battery Duration, in minutes)

        [-rd <000 | 060 | 120 | 180 | 240 | 300 | 360 | 420>] (Return Delay, in seconds)

        [-rsc <00 | 15 | 30 | 45 | 60 | 75 | 90>] (Minimum Return State of Charge, in percent)

        [-sl <0.0 to 359.9>] (Sleep Time, in hours)

Usage: ups  -- Initiate UPS Control

    ups [-c ]

        [-r ] (UPS Runtime Calibration)

        [-s Start] (UPS Selftest)

        [-st] (UPS Status)

        [-a Start] (Test UPS short alarm)

So you'd do something like cfgshutdn -sl 10.0 I think to set the sleep time then ups -c GraceSleep to tell it to gracefully go to sleep when you're ready and it'd observe the 10 hour time you have set and do a graceful sleep assuming you have PowerChute clients you would like to shutdown gracefully prior to the sleep action.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:40 AM . Last Modified: ‎2024-03-13 12:43 AM

0 Likes
0
4102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:40 AM . Last Modified: ‎2024-03-13 12:43 AM

Thank you very much for your answer.   To prevent the high current overshoot from AC source (wall-jacket), I just need follow my former colleague what he does.   Every time, he physically come on site and pressing the button until the UPS (smart 3000) shutdown and he will come back again to restart the UPS by pressing the button, he never unplug/disconnect the power cable from AC source.     What I want do is just doing the same thing,  but remotely.      Can I using “grace sleep” to instead physically come on site to press button ?  What is different affection to the ups and ups battery between sleep and shutdown  (by command)?


Thanks a lot for you help

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:40 AM . Last Modified: ‎2024-03-13 12:43 AM

0 Likes
0
4102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:40 AM . Last Modified: ‎2024-03-13 12:43 AM

I really really appreciate it if you can answer above question at you convenience  !!     smile        By the way , does the  UPS smart 3000XL compatibly with AP9630 ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:40 AM . Last Modified: ‎2024-03-13 12:43 AM

0 Likes
0
4102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:40 AM . Last Modified: ‎2024-03-13 12:43 AM

Thanks a lot , That is really  useful !   But can I disable the alarm that automate inform me when I try to schedule sleep and reboot time by command line.       The alarm  is as below:

Critical Alarm 1 Critical Alarm Present

Graceful Shutdown Initiated

Thanks again

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:40 AM . Last Modified: ‎2024-03-13 12:43 AM

0 Likes
0
4103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:40 AM . Last Modified: ‎2024-03-13 12:43 AM

Disable it how? You won't be able to hide it from the interface but you can likely disable any notifications like SNMP and email.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:41 AM . Last Modified: ‎2024-03-13 12:43 AM

0 Likes
0
4103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:41 AM . Last Modified: ‎2024-03-13 12:43 AM

Sorry, I have been on vacation. If you do a graceful sleep, then yes, this is the same thing your collegue is doing. If AC power is present and you turn the UPS off and don't braindead it (remove AC power and hold down off button to discharge capacitors), then it is in sleep mode. The thing is with either method, someone needs to interact with the UPS to get it to come back on besides in the management card if you set the sleep time in hours. Since your UPS won't be braindead, you'll have access the whole time during this via the AP9630.

Most older Smart UPS beginning with SU, SUM, SUA, SURT, SURTA, and SURT work with AP9630 so a Smart UPS 3000XL of any type will.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:41 AM . Last Modified: ‎2024-03-13 12:43 AM

0 Likes
0
4103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:41 AM . Last Modified: ‎2024-03-13 12:43 AM

Hi

I would like to schedule a specific time to shutdown the UPS and schedule a specific time to restart the UPS by telnet .  for example I want to schedule to shutdown the ups in 8 hours and restart it in 12 hours.

Thanks a lot for any help!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:41 AM . Last Modified: ‎2024-03-13 12:43 AM

0 Likes
0
4103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:41 AM . Last Modified: ‎2024-03-13 12:43 AM

I am only seeing Schedule an action via the web UI under UPS-> Scheduling.

You could do it manually with separate commands though (or by making a script) using the cfgshutdn command and specify the sleep time, in hours, along with ups command to tell it to go to sleep.

Usage: cfgshutdn  -- Configure UPS shutdown parameters

    cfgshutdn [-all] (Show all applicable shutdown parameters for this UPS)

        [-sd <000 | 090 | 180 | 270 | 360 | 450 | 540 | 630>] (Shutdown Delay, in seconds)

        [-lo <02 | 05 | 08 | 11 | 14 | 17 | 20 | 23>] (Low Battery Duration, in minutes)

        [-rd <000 | 060 | 120 | 180 | 240 | 300 | 360 | 420>] (Return Delay, in seconds)

        [-rsc <00 | 15 | 30 | 45 | 60 | 75 | 90>] (Minimum Return State of Charge, in percent)

        [-sl <0.0 to 359.9>] (Sleep Time, in hours)

Usage: ups  -- Initiate UPS Control

    ups [-c ]

        [-r ] (UPS Runtime Calibration)

        [-s Start] (UPS Selftest)

        [-st] (UPS Status)

        [-a Start] (Test UPS short alarm)

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:41 AM . Last Modified: ‎2024-03-13 12:43 AM

0 Likes
0
4103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:41 AM . Last Modified: ‎2024-03-13 12:43 AM

Hi,

I still have 3 questions about the UPS,  Could you please help me to answer it at your convenience?

The reason that we are going to schedule shutdown & schedule restart the UPS is we want to protect the UPS self and connected PC from a high current overshoot when the remote building power on back from an electric problem.

1. By my understanding , the UPS can protect itself from high current overshoot from its AC source (wall-jacket)  and the UPS can ensure a high quality electrical supply to devices.    Am I understanding this right ?

2. I do not understand what the "sleep mode" is , and what different between "sleep mode" and  "manually shutdown" is.   During the sleep period, does the UPS continuity get charging from AC source?

3. What different between using Command line (ups -c gracesleep or sleep) and the Web UI (under UPS-> Scheduling-> One-time Shutdown->Shutdown On/turn back on ) ?

Thanks a lot for your help !!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:41 AM . Last Modified: ‎2024-03-13 12:43 AM

0 Likes
0
4103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:41 AM . Last Modified: ‎2024-03-13 12:43 AM

  1. The UPS has surge protection if that is what we are talking about here. To avoid any issues whatsoever, if it were me I would completely disconnect it from the wall outlet if you have the chance. But if this happened and you had no idea, the UPS is designed to provide surge protection or go to battery power to prevent issues like this and disconnect itself from AC power. High current would most likely cause an undervoltage and also cause the UPS go to battery.
  2. Sleep mode is when the UPS is "sleeping" and waiting for the sleep time duration to expire. As long as AC power is still there, yes, the UPS will trickle charge but its output will be off and the UPS electronics, including the management card will still be on. If you want to avoid this as well, you need to either trip the upstream breaker or input breaker (if your UPS is large enough and has one) so then your UPS will braindead itself but if the AP9630 is braindead, then it cannot be accessible to command the UPS back on remotely.
  3. Command line off commands rely on something external (script, you logging in, etc) to execute the commands. The scheduling feature we offer is a configuration setting you can set and it will store the commands an issue them for you at the date and time you specify. So basically, it is an event you can schedule strictly via the mangement card rather than you writing a script or having to log in. Just another option for users to automate commands who do not have CLI or scripting knowledge and cannot manually do the command when the time comes.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:41 AM . Last Modified: ‎2024-03-13 12:43 AM

0 Likes
0
4103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:41 AM . Last Modified: ‎2024-03-13 12:43 AM

We bought around 280 pieces of 9630 card (v,5.1.7)  and around 30 piece of 9617 (v.3.6.1 ).  sounds all of them are blue web interface

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore