How to read the log and judge where the problem from is ?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How to read the log and judge where the problem from is ?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:36 AM . Last Modified: ‎2024-03-12 02:55 AM

0 Likes
1
1272
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:36 AM . Last Modified: ‎2024-03-12 02:55 AM

How to read the log and judge where the problem from is ?

Someone in my school complained that there was a power outage at this morning 4:10 clock,   Why I can only see one log message regarding the  power outage  "The battery power is too low to support the load; if power fails, the UPS will be shut down immediately."during that time on the UPS

By my understanding of UPS,  the UPS should inform me the "The output power is turned off" in advance of receiving above Log message which is same as it happened at 00:52:11 ,   or provide some information or reason about the power outage .

The UPS  log is as following :

08/26/2014 04:18:14 System: Network service started. System IP is 10.10.117.50 from DHCP server 10.10.10.85 with 518390 second lease.

08/26/2014 04:11:36 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.

08/26/2014 04:11:36 UPS: Restored the local network management interface-to-UPS communication.

08/26/2014 04:11:02 System: Network Interface coldstarted.

08/26/2014 00:52:11 UPS: A low battery condition no longer exists.

08/26/2014 00:52:11 UPS: The output power is turned off.

08/26/2014 00:46:33 UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.

08/26/2014 00:46:33 UPS: On battery power in response to an input power problem.

08/26/2014 00:46:31 UPS: Restored the local network management interface-to-UPS communication.

08/26/2014 00:45:57 System: Network Interface restarted.

08/26/2014 00:28:36 System: Email: Could not resolve 'relay.gxxx.ca'.

08/26/2014 00:26:36 System: Email: Could not resolve 'relay.gxxx.ca'.

08/26/2014 00:24:36 System: Email: Could not resolve 'relay.gxxx.ca'.

08/26/2014 00:19:30 UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.

08/26/2014 00:07:18 UPS: On battery power in response to an input power problem.

08/25/2014 15:36:23 System: NTP update successful.

08/15/2014 22:42:07 System: Email: Could not mail 'relay.gxxx.ca'.

08/15/2014 22:41:54 UPS: Passed a self-test.

08/15/2014 22:41:39 UPS: Started a self-test.

Thanks a lot for help!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:36 AM . Last Modified: ‎2024-03-12 02:55 AM

0 Likes
0
1272
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:36 AM . Last Modified: ‎2024-03-12 02:55 AM

Hello,

For the best possible recommendation/information, I'd suggest that you provide us the full logs if possible, instructions here -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...

Glancing at the small portion you provided, I see this event which you did not highlight in red:

08/26/2014 00:07:18 UPS: On battery power in response to an input power problem.

So, what I am seeing is that there were during the early morning, assuming the time is correct, there was also an outage where the UPS battery was discharged. Thus, if there was another power outage, the UPS hadn't charged up yet. We'll be able to say more when seeing the data log. One think we'll need to know is based on your typical load, how much available battery runtime do you have?

My first guess is that at 00:07:18, the UPS went to battery power. Is your network switch connected to your UPS? I ask because the network interface rebooted and email could not be sent. Then, the Network Management Interface rebooted, perhaps because of the lack of network traffic (a feature of the watchdog mechanism explained here -> Why does my Network Management Card report warmstarts and coldstarts? | FAQs | US) thinking there was an issue with itself possibly and as soon as it did, it realized the UPS was still on battery and runtime was running low. At 00:52:11, the UPS turned off potentially due to running on battery since 00:07:18. At this time, I am thinking the UPS went braindead (de-energized itself completely), waiting for AC power to return so the Network Management Card lost power too. At 04:11:02, it comes back on, indicated by the Network Management Coldstart event (meaning the Network Management Card lost power) and since the UPS hasn't charged up yet since no AC power was available, it reported the battery power was still too low.

This is all an assumption based on looking at this log alone.

Once I see the other logs in conjunction with the full log and understand your typical runtime, I can likely provide a more detailed and concrete response.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:36 AM . Last Modified: ‎2024-03-12 02:55 AM

0 Likes
0
1273
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:36 AM . Last Modified: ‎2024-03-12 02:55 AM

Hello,

For the best possible recommendation/information, I'd suggest that you provide us the full logs if possible, instructions here -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...

Glancing at the small portion you provided, I see this event which you did not highlight in red:

08/26/2014 00:07:18 UPS: On battery power in response to an input power problem.

So, what I am seeing is that there were during the early morning, assuming the time is correct, there was also an outage where the UPS battery was discharged. Thus, if there was another power outage, the UPS hadn't charged up yet. We'll be able to say more when seeing the data log. One think we'll need to know is based on your typical load, how much available battery runtime do you have?

My first guess is that at 00:07:18, the UPS went to battery power. Is your network switch connected to your UPS? I ask because the network interface rebooted and email could not be sent. Then, the Network Management Interface rebooted, perhaps because of the lack of network traffic (a feature of the watchdog mechanism explained here -> Why does my Network Management Card report warmstarts and coldstarts? | FAQs | US) thinking there was an issue with itself possibly and as soon as it did, it realized the UPS was still on battery and runtime was running low. At 00:52:11, the UPS turned off potentially due to running on battery since 00:07:18. At this time, I am thinking the UPS went braindead (de-energized itself completely), waiting for AC power to return so the Network Management Card lost power too. At 04:11:02, it comes back on, indicated by the Network Management Coldstart event (meaning the Network Management Card lost power) and since the UPS hasn't charged up yet since no AC power was available, it reported the battery power was still too low.

This is all an assumption based on looking at this log alone.

Once I see the other logs in conjunction with the full log and understand your typical runtime, I can likely provide a more detailed and concrete response.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of