How to count lines--Configuration file warning: Invalid value on line X

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How to count lines--Configuration file warning: Invalid value on line X
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
114
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
JohnsIsland_apc
Lieutenant JG JohnsIsland_apc
Lieutenant JG

Posted: ‎2021-06-30 04:04 AM . Last Modified: ‎2024-03-08 04:35 AM

0 Likes
7
1868
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:04 AM . Last Modified: ‎2024-03-08 04:35 AM

How to count lines--Configuration file warning: Invalid value on line X

Good Friday morning!

When I see the error, Configuration file warning:: Invalid value on line X, I am not sure which lines to count in the INI file to determine where the problem is.  Do I count lines which are commented out (with a ;), blank lines or head lines (where the line begins with a [ and ends with a ])?

Thanks,

 

Jeff

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JohnsIsland_apc
Lieutenant JG JohnsIsland_apc
Lieutenant JG

Posted: ‎2021-06-30 04:05 AM . Last Modified: ‎2024-03-08 04:35 AM

0 Likes
0
1868
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:05 AM . Last Modified: ‎2024-03-08 04:35 AM

If someone from APC would submit a request to fix the bug I think I found, and so notes this thread, I will mark it as answered/closed.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
JohnsIsland_apc
Lieutenant JG JohnsIsland_apc
Lieutenant JG

Posted: ‎2021-06-30 04:04 AM . Last Modified: ‎2024-03-08 04:35 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:04 AM . Last Modified: ‎2024-03-08 04:35 AM

Another variable, do I count the lines in the INI file I uploaded or should I download the INI file after receiving the error message and count the lines in the downloaded file?

Reply

Link copied. Please paste this link to share this article on your social media post.

JohnsIsland_apc
Lieutenant JG JohnsIsland_apc
Lieutenant JG

Posted: ‎2021-06-30 04:04 AM . Last Modified: ‎2024-03-08 04:35 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:04 AM . Last Modified: ‎2024-03-08 04:35 AM

I cut the file I was uploading so I could whittle away and figure out which line was bad.  I received the same error messages including invalid value on line 23.  Given the file below, I think the error message is reporting what's bad in the file running on the NMC.  Will downloading the INI file and counting lines (which lines) give me the error lines?  Or is the invalid value on line X not related to a line in the INI file?

 

One way to fix the problem is to download from a different NMC, upload it to make sure it doesn't generate invalid values, modify it if nessecary, and upload it to the NMC that is returning invalid values after uploading.  Yes, I did make more than one change at a time and didn't keep a copy of the file before I made multiple changes.  Hopefully I will remember to keep a copy of the INI and/or make one change at a time.

Jeff

; Schneider Electric
; Network Management Card AOS v6.6.4
; Smart-UPS & Matrix-UPS APP v6.6.4
; (c) Copyright 2003 - 2018 All Rights Reserved
; Configuration file, generated on 11/07/2018 at 21:13:03 by Administrator apc

[NetworkTCP/IP]

IPv4=enabled
BootMode=DHCP Only
DomainName=bmain.bsf
PortSpeed=Auto
DHCPBootpVendorClass=APC
DHCPBootpClientID=MAC
DHCPBootpUserClass=SUMX
DHCPRequireCookie=disabled
PingResponse=enabled
IPv6=disabled
IPv6DefaultGateway=::
IPv6IP=::/64
IPv6Manual=disabled
IPv6AutoConfig=enabled
DHCPv6Mode=Router Controlled

 

Reply

Link copied. Please paste this link to share this article on your social media post.

JohnsIsland_apc
Lieutenant JG JohnsIsland_apc
Lieutenant JG

Posted: ‎2021-06-30 04:04 AM . Last Modified: ‎2024-03-08 04:35 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:04 AM . Last Modified: ‎2024-03-08 04:35 AM

I have been testing to see if I can clear the errors by formatting and uploading firmware. Testing with a SUA750XL and a AP9630.  I have formatted by pressing the reset button until I see the right NIC LED flashing orange.  After formatting I have uploaded the same F/W (6.6.4).  I then download and upload the config.ini using the ini utility.  After the upload is complete, I open the device log file and find the errors listed below.

How do I resolve the errors I am finding? 

 

 09/16/2019 12:22:47 apc Web user 'apc' logged in from 172.26.106.66.
 09/16/2019 12:22:46 System Configuration file upload complete, with 895 valid values.
 09/16/2019 12:21:42 System Configuration file warning: Invalid value on line 369.
 09/16/2019 12:21:42 System Configuration file warning: Invalid value on line 367.
 09/16/2019 12:21:42 System Configuration file warning: Invalid value on line 366.
 09/16/2019 12:21:42 System Configuration file warning: Invalid value on line 365.
 09/16/2019 12:21:41 System Configuration file warning: Invalid value on line 364.
 09/16/2019 12:21:41 System Configuration file warning: Invalid value on line 363.
 09/16/2019 12:21:41 System Configuration file warning: Invalid value on line 362.
 09/16/2019 12:21:41 System Configuration file warning: Invalid value on line 361.
 09/16/2019 12:21:41 System Configuration file warning: Invalid value on line 360.
 09/16/2019 12:21:41 System Configuration file warning: Invalid value on line 359.
 09/16/2019 12:21:41 System Configuration file warning: Invalid value on line 358.
 09/16/2019 12:21:41 System Configuration change. Event log web display filter category.
 09/16/2019 12:21:40 System Configuration change. Event log web display filter severity.
 09/16/2019 12:21:37 System Configuration change. System name.
 09/16/2019 12:21:32 System Configuration change. Host name.
 09/16/2019 12:21:31 apc FTP user 'apc' logged out from 172.26.106.66.
 09/16/2019 12:21:28 apc FTP user 'apc' logged in from 172.26.106.66.
 09/16/2019 12:21:28 apc FTP user 'apc' logged out from 172.26.106.66.
 09/16/2019 12:21:28 apc FTP user 'apc' logged in from 172.26.106.66.
 09/16/2019 12:20:45 apc FTP user 'apc' logged out from 172.26.106.66.
 09/16/2019 12:20:28 apc FTP user 'apc' logged in from 172.26.106.66.
 09/16/2019 12:20:28 apc FTP user 'apc' logged out from 172.26.106.66.
 09/16/2019 12:20:28 apc FTP user 'apc' logged in from 172.26.106.66.
 09/16/2019 12:19:42 apc FTP user 'apc' logged out from 172.26.106.66.
 09/16/2019 12:19:23 apc FTP user 'apc' logged in from 172.26.106.66.
 09/16/2019 12:19:23 apc FTP user 'apc' logged out from 172.26.106.66.
 09/16/2019 12:19:23 apc FTP user 'apc' logged in from 172.26.106.66.
 09/16/2019 12:17:41 Device UPS: Restored the local network management interface-to-UPS communication.
 09/16/2019 12:17:37 System Network service started. System IP is 172.26.222.84 from DHCP server 172.26.106.62 with 604790 second lease.
 09/16/2019 12:17:24 System Network service started. IPv6 address FE80::2C0:B7FF:FED7:2CF2 assigned by link-local autoconfiguration.
Reply

Link copied. Please paste this link to share this article on your social media post.

JohnsIsland_apc
Lieutenant JG JohnsIsland_apc
Lieutenant JG

Posted: ‎2021-06-30 04:04 AM . Last Modified: ‎2024-03-08 04:35 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:04 AM . Last Modified: ‎2024-03-08 04:35 AM

I forgot to mention, when downloading the file it takes about 20-22 seconds.  When uploading it takes 3-4 seconds.  Is the upload process terminating early due to corruption?

Reply

Link copied. Please paste this link to share this article on your social media post.

JohnsIsland_apc
Lieutenant JG JohnsIsland_apc
Lieutenant JG

Posted: ‎2021-06-30 04:04 AM . Last Modified: ‎2024-03-08 04:35 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:04 AM . Last Modified: ‎2024-03-08 04:35 AM

I found the 6.8 F/W upgrade today.  I formatted a AP9630, then to 6.8, and found only one invalid value after using the ini utility.  I need to test a bit more, as I am working on a different AP9630 card today.  Hopefully the F/W update is the cause for the reducing the invalid values.

It would be nice if someone from APC would weigh in on the problems I have/am seeing.

Kind of curious why the 6.8 is in a different section of the AP9630 download page.

Jeff

Reply

Link copied. Please paste this link to share this article on your social media post.

JohnsIsland_apc
Lieutenant JG JohnsIsland_apc
Lieutenant JG

Posted: ‎2021-06-30 04:04 AM . Last Modified: ‎2024-03-08 04:35 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:04 AM . Last Modified: ‎2024-03-08 04:35 AM

After updating a AP9631 to v6.8.0/v6.8.2/v1.0.9 in a SMX2000LV with UPS 07.4 (ID1003), I downloaded the user config file and uploaded the same user config file and found only one error: SystemConfiguration file warning: Invalid value on line 239.  That is quite an improvement.

Just for fun, I copied the aforementioned user config file into Excel, and found line 239: DeviceCommCtrl="", which is in the NetworkBACnet section.  I don't have a clue if that is the problem line or if the problem line is elsewhere.  I did see a possible error in the BACnet/IP GUI, the check box is on the line above Enable foreign device registration. 

I just enabled BACnet, and had to enter a password.  I downloaded the config file and uploaded the same config file.  Amazing, the Invalid value on line 239 error did not appear.  I then disabled BACnet, downloaded and uploaded the file and the error did not appear.  I think this means the NIC doesn't like an empty value in DeviceCommCtrl="".  

I would ask APC to fix this itty bitty error.  Until APC fixes the error, I will add a valid password to the user config file so the APC Events log is clean, in order to satisfy my A/R desire to ensure I don't have any errors which could cause problems with mission critical equipment. 

Jeff

 

Reply

Link copied. Please paste this link to share this article on your social media post.

JohnsIsland_apc
Lieutenant JG JohnsIsland_apc
Lieutenant JG

Posted: ‎2021-06-30 04:05 AM . Last Modified: ‎2024-03-08 04:35 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:05 AM . Last Modified: ‎2024-03-08 04:35 AM

If someone from APC would submit a request to fix the bug I think I found, and so notes this thread, I will mark it as answered/closed.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of