How to Maintain 30% Load

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How to Maintain 30% Load
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Coaster1200
Crewman Coaster1200
Crewman

Posted: ‎2022-12-02 05:12 AM

1 Like
6
2006
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-02 05:12 AM

How to Maintain 30% Load

I have just replaced the UPS batteries in my SmartUPS1000 (2005 model) and am having the charge lights constantly flashing and a zero minutes run-time.  I have tried the recalibration in Powerchute (v9 and 10) and, last night ran the manual calibration.  All with no joy.  The only thing that I am not 100% sure of is whether the load fell below the 30% figure given.

The procedure for manual recalibration requires:

  • There must be at least a 30% load attached to the UPS during this procedure, and this load cannot fluctuate more than +/- 5%. THIS IS IMPORTANT

FYI: I set my load to the computer (11 to 13%), a 60W heater, and a power drill set to a low speed to get me to around the 35% figure.  This seemed fairly constant while I monitored before I unplugged the USB lead and the mains supply.  The drill etc ran for a good 20 minutes (I didn't time it) but after leaving the UPS on charge overnight, I still have 0 minutes of runtime remaining in Powerchute and flashing charge level lights.

Does anyone have any tips for making sure the load percentage is 30% minimum and within +/-5%?  I would like to make sure of this before I try again.  Or, is there something else I can try?  

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-12-15 04:50 AM

0 Likes
2
1932
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-15 04:50 AM

Hi @Coaster1200 

 

Based on the serial number, I am guessing that your UPS could be an SU/SUA/SURTA model that has encountered the issue mentioned in the FAQ article below:

 

Why are the battery charge LEDs flashing on a Smart-UPS? (FA156538) 

 

The FAQ outlines the recommended steps to address the issue and as mentioned, if it couldn't be resolved you would have to reach out to our Technical Support.  In my experience, for SU/SUA units there is something that we call as CalKey which we send to our customer, not sure though if this is still available since the UPS has been phased out for quite some time now.

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Coaster1200
Crewman Coaster1200
Crewman

Posted: ‎2022-12-18 11:53 AM

In response to JonPro
0 Likes
1
1924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-18 11:53 AM

Many thanks for the reply.  It went to my Junk Mail folder and I have only just seen it.

I followed the FAQ before.  Options 1 and 2 didn't work and I have tried Option 3 but don't know how to make sure I always have a minimum of 30% load.  I ran an electric drill to get my overall load above 30% (including the computer load).  This didn't reset the runtime calibration and Schneider has now said that it is not advisable to use a drill but has failed to tell me what is advisable as load except "computer equipment".  Most of that is a pretty variable load in my experience and the FAQ says I need to keep the load within +/-5%.

FYI: the runtime remaining is always shown as zero minutes in Powerchute but when I have done the manual calibration, the computer stays on for well over 20 minutes (with the drill running).  The batteries are brand new.  I will try again one day in the hope that Einstein was wrong - “Insanity is doing the same thing over and over and expecting different results.”

 

Reply

Link copied. Please paste this link to share this article on your social media post.

JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-12-19 08:43 PM

In response to Coaster1200
0 Likes
0
1907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-19 08:43 PM

I am sorry to hear that @Coaster1200.  If both Manual and Software calibration didn't solve the issue my next guess would be that it is an issue with the EPROM of the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Coaster1200
Crewman Coaster1200
Crewman

Posted: ‎2022-12-20 06:08 AM

0 Likes
1
1905
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-20 06:08 AM

Is there a way of verifying please that without buying a new UPS?

Reply

Link copied. Please paste this link to share this article on your social media post.

JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-12-20 05:05 PM

In response to Coaster1200
0 Likes
0
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-20 05:05 PM

From the behavior that the UPS is showing, it is an indicator that there is an issue with the EPROM.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

shimonp
shimonp
Cadet

Posted: ‎2023-03-30 10:17 AM

0 Likes
0
1755
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-30 10:17 AM

What can be done to resolve EPROM issue? APC UPS costs small fortune and we expect a better performance from the unit. In my case I have similar model with similar issue - Smart UPS 1500. Nothing I do is fixing flashing lights.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore