How to Automatically Shutdown UPS when Temperature reaches the Threshold

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How to Automatically Shutdown UPS when Temperature reaches the Threshold
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:40 AM . Last Modified: ‎2024-03-13 01:36 AM

0 Likes
8
3628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:40 AM . Last Modified: ‎2024-03-13 01:36 AM

How to Automatically Shutdown UPS when Temperature reaches the Threshold

Hello,

I want to ask that how can computers on UPS shutdown automatically when environment temperature Threshold reaches 30 Centigrade (Having Model number: SRCPM6K1 & Serial Number:6S1513Z00444).

Please Help.

Thank you.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • apc
  • cooling
  • power
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 04:41 AM . Last Modified: ‎2024-03-13 01:35 AM

0 Likes
0
3621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:41 AM . Last Modified: ‎2024-03-13 01:35 AM

It's also that available battery capacity decreases due to age. So 20% left might provide 10 minutes of power on a new battery but only 5 minutes on an older battery. And it's the time that matters.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:40 AM . Last Modified: ‎2024-03-13 01:35 AM

0 Likes
0
3621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:40 AM . Last Modified: ‎2024-03-13 01:35 AM

Hi   Osama,

In order to enable environmental temperature monitoring, the UPS needs   to be equipped with an AP9631 Network Management Card. The required AP9335T temp sensor comes included with the NMC, and the acceptable temp thresholds can be configured in the NMC   web interface. The   PowerChute   Network Shutdown   clients installed on the computers can then be configured to initiate OS shutdown if the environmental probe readings are out of the configured tolerances.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:40 AM . Last Modified: ‎2024-03-13 01:35 AM

0 Likes
0
3621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:40 AM . Last Modified: ‎2024-03-13 01:35 AM

Hey,

Thank you for responding.We already have "Network Management Card" Installed that you mentioned in your post.We have also done Configuration to initiate Shutdown if Battery is about to Run Out using "POWERCHUTE Software" !But how can we achieve OS Shutdown  "If environmental Probe Readings are out of the Configured Tolerances(Specifically for Temperature).Looking forward to your Suggestion.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:40 AM . Last Modified: ‎2024-03-13 01:35 AM

0 Likes
0
3621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:40 AM . Last Modified: ‎2024-03-13 01:35 AM

Hi Osama,

If there is an AP96335T temperature probe connected to the Universal I/O port 1 of the AP9631, the temp thresholds can be configured and enabled under NMC  section Configuration->Universal I/O->Temp & Humidity->Port 1 Temp 1. Once the probe is connected, the PowerChute  event  Temperature Probe 1 Out Of Range will be available in the Configure  Events section.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:40 AM . Last Modified: ‎2024-03-13 01:35 AM

0 Likes
0
3621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:40 AM . Last Modified: ‎2024-03-13 01:35 AM

Hey SVS,

            Ok.so The thing is how can temp thresholds be configured and enabled under NMC  section Configuration->Universal I/O->Temp & Humidity? 😞 Following is the Screen shot of it. We have configured the setting from PowerChute Software Successfully.

Thanx again!

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:40 AM . Last Modified: ‎2024-03-13 01:35 AM

0 Likes
0
3621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:40 AM . Last Modified: ‎2024-03-13 01:35 AM

Hi Osama,

The 4 temperature thresholds are already enabled (ticked) in your screen shot. If you need shutdown at 30 C degrees, set the Maximum value to 30. Once this threshold is exceeded,  PowerChute will initiate OS shutdown based on  Temperature Probe 1 Out Of Range event.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:40 AM . Last Modified: ‎2024-03-13 01:35 AM

0 Likes
0
3621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:40 AM . Last Modified: ‎2024-03-13 01:35 AM

Hey SVS,

Thankyou so much for your help.We have applied all "the Required settings".But i was thinking ,If I could "Initiate" the OS shuts down when Battery is remained "20%" ( UPS goes to Sleep mode).Finally when battery power Reaches back to "30%" (UPS also goes Online).Need Help.

Thanks a lot again 🙂 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:41 AM . Last Modified: ‎2024-03-13 01:35 AM

0 Likes
0
3621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:41 AM . Last Modified: ‎2024-03-13 01:35 AM

Hi Osama,

The available PowerChute events are all available in the Configure Events section. For shutdown based on run-time, the threshold is configurable in time, rather than in battery charge %. The useful  choice here would be <Runtime remaining below threshold>. 

The Return from Shutdown behavior in turn needs to be configured in the NMC  web interface, in the Configuration -> Shutdown -> End of Shutdown section. Here too, the return delay is  based on Available run-time (Return Runtime Duration) rather than Available battery charge %.

This is most likely the case because OS shutdown durations are usually defined in minutes, so  it makes it easier to relate available run-time to this than available battery  charge %.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 04:41 AM . Last Modified: ‎2024-03-13 01:35 AM

0 Likes
0
3622
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:41 AM . Last Modified: ‎2024-03-13 01:35 AM

It's also that available battery capacity decreases due to age. So 20% left might provide 10 minutes of power on a new battery but only 5 minutes on an older battery. And it's the time that matters.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.