How much power an UPS requires to run itself ?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How much power an UPS requires to run itself ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:37 AM . Last Modified: ‎2024-03-12 03:36 AM

0 Likes
2
2268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:37 AM . Last Modified: ‎2024-03-12 03:36 AM

How much power an UPS requires to run itself ?

Hi All,

I have a APC SU 700 INET UPS, 750VA/450W. It is customized to work with 24V. I think so because I haven't found this model to be a 24V yet and it doesn't run with one 12V battery. I am using it with 2 x 12V/45 AMP batteries (connected serially to produce 24V). Place where I live, you might find it interesting, in the meaning, there is almost 12 hours power outage every single day. So, I know the UPS itself in no way would be able to charge those batteries in the given hours of electricity. So, I've hooked 2x12V/40w Solar Panels (serially to produce 24V)  to have those batteries charged. The New batteries are one year old and worked very well during the first year. Now, it has become frequent that I get low battery indicator On, and the battery voltage drops down to 11.90, and I have to shut down the UPS. I have several questions in my mind :

  1. Are those batteries not getting enough charge that it could support load ? The load is not much, during day it is pretty much just one laptop whose adapter reads Output 18.5W 3.5 Amp, other than that 2x 20W CFL bulbs use the power for about 5 hrs at the most during evening.
  2. At what rate my UPS charges the batteries, in Amp/hr while there is electricity ?
  3. The solar panel I use reads [Max Power : 40w ; Operating Voltage : 17.2 V ; Operating Current : 2.32 A ; Open Circuit Voltage : 2.16 V ; Short Circuit Current 2.57 A]. During day, when sun is bright it reads around 27VDC at the charge controller, tested with digital multi-meter, during this time at what rate it charges the battery (in Amp/hr) ?

And important of all

How much power (Amp/hr) my UPS requires just to run itself (without any load) while running in batteries ?

Thank you for your time and support.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:37 AM . Last Modified: ‎2024-03-12 03:36 AM

0 Likes
0
2267
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:37 AM . Last Modified: ‎2024-03-12 03:36 AM

This UPS is very old and discontinued so what I can contribute is for the load losses (at zero load) to give you an idea of what the power consumption of the UPS all by itself is. I think this will also assume a fully charged battery.

Bellow is the tool for the UPS Efficiency Comparison Calculator. I would suggest looking at the most similar model to this UPS to get an idea. Newer UPSs are a little bit more efficient but this will give you an idea that is close to what your UPS utilizes. SUA750I is the replacement for SU700INET so I'd suggest using that and comparing it against itself and dragging the load percentage to 0%.

http://www.apc.com/tool/?tt=5

I see the answer for this UPS at 17W and it will be a little more if it is charging the batteries as well but it sounds like you're not using the charger)

2171_sua750I.jpg

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:37 AM . Last Modified: ‎2024-03-12 03:36 AM

0 Likes
0
2267
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:37 AM . Last Modified: ‎2024-03-12 03:36 AM

Hi All,

I have a APC SU 700 INET UPS, 750VA/450W. It is customized to work with 24V. I think so because I haven't found this model to be a 24V yet and it doesn't run with one 12V battery. I am using it with 2 x 12V/45 AMP batteries (connected serially to produce 24V). Place where I live, you might find it interesting, in the meaning, there is almost 12 hours power outage every single day. So, I know the UPS itself in no way would be able to charge those batteries in the given hours of electricity. So, I've hooked 2x12V/40w Solar Panels (serially to produce 24V)  to have those batteries charged. The New batteries are one year old and worked very well during the first year. Now, it has become frequent that I get low battery indicator On, and the battery voltage drops down to 11.90, and I have to shut down the UPS. I have several questions in my mind :

  1. Are those batteries not getting enough charge that it could support load ? The load is not much, during day it is pretty much just one laptop whose adapter reads Output 18.5W 3.5 Amp, other than that 2x 20W CFL bulbs use the power for about 5 hrs at the most during evening.
  2. At what rate my UPS charges the batteries, in Amp/hr while there is electricity ?
  3. The solar panel I use reads [Max Power : 40w ; Operating Voltage : 17.2 V ; Operating Current : 2.32 A ; Open Circuit Voltage : 2.16 V ; Short Circuit Current 2.57 A]. During day, when sun is bright it reads around 27VDC at the charge controller, tested with digital multi-meter, during this time at what rate it charges the battery (in Amp/hr) ?

And important of all

How much power (Amp/hr) my UPS requires just to run itself (without any load) while running in batteries ?

Thank you for your time and support.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:37 AM . Last Modified: ‎2024-03-12 03:36 AM

0 Likes
0
2268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:37 AM . Last Modified: ‎2024-03-12 03:36 AM

This UPS is very old and discontinued so what I can contribute is for the load losses (at zero load) to give you an idea of what the power consumption of the UPS all by itself is. I think this will also assume a fully charged battery.

Bellow is the tool for the UPS Efficiency Comparison Calculator. I would suggest looking at the most similar model to this UPS to get an idea. Newer UPSs are a little bit more efficient but this will give you an idea that is close to what your UPS utilizes. SUA750I is the replacement for SU700INET so I'd suggest using that and comparing it against itself and dragging the load percentage to 0%.

http://www.apc.com/tool/?tt=5

I see the answer for this UPS at 17W and it will be a little more if it is charging the batteries as well but it sounds like you're not using the charger)

2171_sua750I.jpg

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore