How many amp/h do I need for 3KW for 15 hours?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How many amp/h do I need for 3KW for 15 hours?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-25 10:52 PM . Last Modified: ‎2024-03-19 03:25 AM

0 Likes
5
4393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 10:52 PM . Last Modified: ‎2024-03-19 03:25 AM

How many amp/h do I need for 3KW for 15 hours?

I have a 10KW solar installation to offset the cost of a 3KW server room.

I am thinking of installing some batteries to supplement a solar installation for night time use.
The solar install was larger than I needed in order to offset low wattage days, or, when the sun didn't shine as strongly if you will. All I need is about 3KW from the install.

Anyhow, I am trying to calculate what I would need in terms of amp/h in order to never kill my batteries, yet be able to run the full load off of them during night time hours.

So, that equates to about 15hrs at 3KW/h. It's probably simpler than I am making it in my mind but I've confused myself so figured, time to post and ask pros smile

Thank you!

Labels
  • Labels:
  • Server Room & Data Center Design Best Practices
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-25 10:52 PM . Last Modified: ‎2024-03-19 03:24 AM

0 Likes
0
4393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 10:52 PM . Last Modified: ‎2024-03-19 03:24 AM

You need 3KW power for 15 hours. Right?

To estimate the AH rating of the battery system, Kindly share the DC operating voltages of the system in use please.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-25 10:52 PM . Last Modified: ‎2024-03-19 03:25 AM

0 Likes
0
4393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 10:52 PM . Last Modified: ‎2024-03-19 03:25 AM

HI in order to attempt to answer your question a bit of additional information would be helpful:


What is the size/capacity and efficiency of the Inverter/Solar Charge Controller you chose for the solar backup power system ?

Are you using the solar system as a "B" power source to reduce the hydro power drawn by the servers (IE the servers all have dual power supplies) ?

Or is it a complete switchover to the battery/inverter at night via a transfer switch of some sort ?

I gather you are needing / thinking deep cycle batteries if you are going to run them down significantly overnight every single night ?


Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-25 10:52 PM . Last Modified: ‎2024-03-19 03:24 AM

0 Likes
0
4393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 10:52 PM . Last Modified: ‎2024-03-19 03:24 AM

All of the servers have redundant two and three power supplies and everything is on an APC UPS which is then tied to the grid along with a transfer switch for generator backup.

The solar setup is a 10KW system, I can't give you it's efficiency really and there is no inverter at the moment, I would need to add one.

As mention in my original post however, I only need 3KW but wanted to make as sure as I could that even on low sun days, I might have a good chance of getting at least what I need.

Right now, the setup simply feeds back to the power company which in turn credits our account. The panels have inverters built in so the array puts out 240V at x watts depending on sun, all A/C. I would add batteries in order to run the server room in evening hours off of the batteries. I would use more battery than I need to make sure they never get fully depleted. I haven't thought about how I would switch the power in or out yet but probably an automated switch which can be time controlled. That way, even if there isn't enough power, it would know to switch back to utility. All of this would be pre-UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-25 10:52 PM . Last Modified: ‎2024-03-19 03:24 AM

0 Likes
0
4393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 10:52 PM . Last Modified: ‎2024-03-19 03:24 AM

I did a back of the envelope calculation based on say 90% inverter efficiency (which is a bit on the bottom end I suppose), and utilizing 12 volt cells you would need just over 4,000 Amp-Hours worth of batteries to go 15 hours at 3,000 watts:

3kW x 15 Hrs = 45 kWH  .... divide that by 12 volts = 3750 AH ...divide that by .90 for efficiency gets you 4,200 AH.... if you take the average car battery at say 60 to 75 AH capacity you would need the equivalent of 55 to 60 of them to last the night.

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-25 10:52 PM . Last Modified: ‎2024-03-19 03:24 AM

0 Likes
0
4393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 10:52 PM . Last Modified: ‎2024-03-19 03:24 AM

I had a setup which had 20 12VDC marine batteries hooked to it's own smart charging system which was being used with a 18K USP a few years back.

At one point, it ran on battery for over 7hrs until the power came back. Those 20 batteries were a pain to maintain so I can't imagine 60 batteries.

However, maybe I could look at very large solar batteries, maybe 48VDC or something with lots of HA, combined or something.

This is interesting and doesn't sound very doable now.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-25 10:52 PM . Last Modified: ‎2024-03-19 03:24 AM

0 Likes
0
4394
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 10:52 PM . Last Modified: ‎2024-03-19 03:24 AM

You need 3KW power for 15 hours. Right?

To estimate the AH rating of the battery system, Kindly share the DC operating voltages of the system in use please.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of