Help with Smart-UPS 1000VA XL 230V needed.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Help with Smart-UPS 1000VA XL 230V needed.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:35 PM . Last Modified: ‎2024-03-14 04:18 AM

0 Likes
1
663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:35 PM . Last Modified: ‎2024-03-14 04:18 AM

Help with Smart-UPS 1000VA XL 230V needed.

Hi everyone. I actually got this for free from a friend; it's a brand new unit. I figured I'd use it as opposed to trying to sell it since I get very brief power outages pretty often...the problem seems to be that it's a 230V model and while it seems to charge when I plug it into an outlet, as soon as I actually test a computer by turning it on and pressing the start button,the computer will not start. If I instead press and hold the test/start button, the fan comes on on the UPS and then if I press the power button on the computer, it starts but the UPS keeps beeping because it seems to supply only battery power. It seems that the UPS for some reason charges the battery but it's unable to supply power from the wall to whatever is connected to the UPS. Any ideas?I live in the US in an apt building and I think it may have something to to with the voltage rating...

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:35 PM . Last Modified: ‎2024-03-14 04:18 AM

0 Likes
0
663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:35 PM . Last Modified: ‎2024-03-14 04:18 AM

First of all, the 230 Vac product is not designed to work in the U.S. It outputs 230 Vac on the outlets which will not power 120 Vac product. What is the input voltage does the Computer require? Does it require 120 Vac? If so, this 230 Vac product will not work with your 120 Vac equipment.

Please view the below k-base document which explains why a 230 Vac international model Smart-UPS should not be used in North America.
[http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=1016]

I hope that this helps.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:35 PM . Last Modified: ‎2024-03-14 04:18 AM

0 Likes
0
664
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:35 PM . Last Modified: ‎2024-03-14 04:18 AM

First of all, the 230 Vac product is not designed to work in the U.S. It outputs 230 Vac on the outlets which will not power 120 Vac product. What is the input voltage does the Computer require? Does it require 120 Vac? If so, this 230 Vac product will not work with your 120 Vac equipment.

Please view the below k-base document which explains why a 230 Vac international model Smart-UPS should not be used in North America.
[http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=1016]

I hope that this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore