Hi there.
Wanting some help figuring out which cables I need to connect my Smart UPS 3000 (smx300RMHV2U) to the external battery pack (3000RMI2U). It came without the cables so having a hard time figuring out what I need.
Got the 15 amp plugs for mains. But nothing to connect the 2.
Did try the output from UPS to input on Pack, but no luck.
Also yes I did check the manual but it did not help me much figuring it out. Its unclear to me. I assume I need to plug from the connector marked in Green to an input on the battery pack. But not sure where either.
Any help be appreciated. Clearly not an expert on UPS 🙂rkAtcUNLGS%2FBADfMV%2B7y4g%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg
Battery packDMhNQu6p1oruveGDHGp44Q%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:50 AM . Last Modified: 2024-03-15 04:20 AM
No worries,
I think SMX120BP is what your looking for but it should be in the manual.
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:49 AM . Last Modified: 2024-03-15 04:20 AM
Hi Harry,
That's not a UPS and a battery pack, that's two UPSs.
Battery packs don't have power sockets or Smart Slots.
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:50 AM . Last Modified: 2024-03-15 04:20 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:50 AM . Last Modified: 2024-03-15 04:20 AM
I'll be darned. Received some wrong info in that case.
That does explain why I could not figure out the manual on connecting it either.
Thanks for the input.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:50 AM . Last Modified: 2024-03-15 04:20 AM
No worries,
I think SMX120BP is what your looking for but it should be in the manual.
-Gavan