Help!! I need 8 hours of battery backup!

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Help!! I need 8 hours of battery backup!
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:13 AM . Last Modified: ‎2024-03-08 01:23 AM

0 Likes
4
5484
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:13 AM . Last Modified: ‎2024-03-08 01:23 AM

Help!! I need 8 hours of battery backup!

My company is installing a network system in a very remoter location and we must have 8 hours of backup battery power.

The backup system must be able to support the following:

One router: Power consumption is 160 w max and input current is 4A @ 110VAC
One switch: Power consumption is 148 w max and input current is 1.2A max
Five internet access devices: Power consumption for each is 1.2A 70W

Am I correct to say that the total maximum power requirements for the above system is 658 watts per hour? If so, what type of APC arrangement would met my needs?

Sorry, my user name is " LikeAPro", however, I am very new to this.

I would appreciate any help on this matter.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:13 AM . Last Modified: ‎2024-03-08 01:23 AM

0 Likes
0
5483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:13 AM . Last Modified: ‎2024-03-08 01:23 AM

Thanks!

A generator would be great, however this site location is extremely remote and getting a service tech there with a generator could take 6 to 8 hours.

Where I go to plug in the total watts and hours to come up with the sizing requirements?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: ‎2021-06-30 06:13 AM . Last Modified: ‎2024-03-08 01:23 AM

0 Likes
0
5483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:13 AM . Last Modified: ‎2024-03-08 01:23 AM

You can size based on your Watt values as long as they are Max values.

Generally speaking though, if you want 8 hours of backup, the common method would be to have a battery back-up to handle the initial power outage until a generator can kick in to supply extended runtime.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:13 AM . Last Modified: ‎2024-03-08 01:23 AM

0 Likes
0
5484
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:13 AM . Last Modified: ‎2024-03-08 01:23 AM

Thanks!

A generator would be great, however this site location is extremely remote and getting a service tech there with a generator could take 6 to 8 hours.

Where I go to plug in the total watts and hours to come up with the sizing requirements?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:13 AM . Last Modified: ‎2024-03-08 01:23 AM

0 Likes
0
5483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:13 AM . Last Modified: ‎2024-03-08 01:23 AM

Hi,

I used the selector here and it provided some 120V matches.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:13 AM . Last Modified: ‎2024-03-08 01:23 AM

0 Likes
0
5483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:13 AM . Last Modified: ‎2024-03-08 01:23 AM

likeapro wrote:
Thanks!

A generator would be great, however this site location is extremely remote and getting a service tech there with a generator could take 6 to 8 hours.

Where I go to plug in the total watts and hours to come up with the sizing requirements?
It would be the same to get a service tech to maintain the UPS, wouldn't it? For your loads, SUA1500 should be adequate to carry the load.

With a generator, the power goes out, UPS instantly provides power for up to a minute or so needed for generator to start up and stabilize. Once the generator is running, automatic transfer switch provides power to UPS input.

Get a generator with automatic self-test with visible error status display and you can use an IP-camera aimed at the control panel to check on it remotely.

Although your IT equipment will operate fine on generator power, Smart-UPS is extremely sensitive to frequency deviation, so it might unnecessarily reject your generator.

If that's the case, the online Smart-UPS RT should work better.
http://www.apcc.com/resource/include/techspec_index.cfm?base_sku=SURTA1500XL&total_watts=50

If natural gas connection is available, it will provide power as long as gas is available. If not, you'll have to find someone to refuel the tank.

If you go with 8-hours of battery based backup, the recurring expense of changing out 8 hours worth of battery will get quite costly.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore