Has APC got any failure rates (%) by age statistics on their batteries?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Has APC got any failure rates (%) by age statistics on their batteries?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:00 AM . Last Modified: ‎2024-03-13 11:35 PM

0 Likes
1
2172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:00 AM . Last Modified: ‎2024-03-13 11:35 PM

Has APC got any failure rates (%) by age statistics on their batteries?

Hi UPS Experts!

We have just deployed about 100 UPSs (2200 RM and X 1500) and now need to budget for proactive battery replacements down the road.

APC states that battery life expectency is 3-5 years. With such a large deployment of UPSs, the savings can be considerable if we stretch battery replacement out to 5 years but we don't want to do that if half of them will die prior to their replacement! At the same time, we don't want to replace the batteries every 3 years if they are still performing well and have some life left in them.

If failure rate stats were available then we could make an informed decision. For instance, if typical (ie. under normal operating conditions) failure rates were 2%, 3%, 5% for years 3, 4, and 5 then we would probably go with 5 years. But if it jumped to 25% in the 5th year, then we would go with battery replacement every 4 years.

Please don't respond "it depends". I know there are several factors that determine how long a battery actually will last. I'm just wondering if large field tests have been done and what the results were. These don't necessarily have to be APC results. Since UPS batteries are UPS batteries, even stats from another UPS vendor or 3rd party would suffice.

Thanks for your response. Ian.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:00 AM . Last Modified: ‎2024-03-13 11:35 PM

0 Likes
0
2173
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:00 AM . Last Modified: ‎2024-03-13 11:35 PM

I look after about 300 apc ups , the majority being SUA3000's and also have 8 Symmetra PX40's and 80's' ... in my experience the biggest factor in battery life expectancy is how cool the environment is your ups is operating in: Eg in my Data center where I've got 16 Celcius air to the racks, the batteries in my Smart-UPS and Symmetra PX's have lasted up to 6 to 8 years. I have Matrix UPS with Panasonic cells in them that are 9 to 10 years old now and still passing the self tests and doing their job. BUT, out in comm rooms where there is poor ventilation and the ups is running in 26 , 27, 28 or even 30 plus Celcius temperature range, the battery life can be as little as 3 years, per the bottom end of the APC spec.
Dave

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:00 AM . Last Modified: ‎2024-03-13 11:35 PM

0 Likes
0
2174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:00 AM . Last Modified: ‎2024-03-13 11:35 PM

I look after about 300 apc ups , the majority being SUA3000's and also have 8 Symmetra PX40's and 80's' ... in my experience the biggest factor in battery life expectancy is how cool the environment is your ups is operating in: Eg in my Data center where I've got 16 Celcius air to the racks, the batteries in my Smart-UPS and Symmetra PX's have lasted up to 6 to 8 years. I have Matrix UPS with Panasonic cells in them that are 9 to 10 years old now and still passing the self tests and doing their job. BUT, out in comm rooms where there is poor ventilation and the ups is running in 26 , 27, 28 or even 30 plus Celcius temperature range, the battery life can be as little as 3 years, per the bottom end of the APC spec.
Dave

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore