Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

HYSTERESIS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • HYSTERESIS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

0 Likes
6
3386
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

HYSTERESIS

Hi everyone,

Good day. I was just wondering, could someone please help me with this. I can't seem to understand its purpose. It's in the web browsing of the SRT5KRMXLI UPS. What is the purpose of HYSTERESIS in the Temperature Threshold of the unit. I attached the screenshot for you to see. Does it have something to do with heat dissipation? Please enlighten me, your response is appreciated. Thanks!

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

0 Likes
0
3389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

Thanks Voidstar.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

0 Likes
0
3389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

Hysteresis is the property by which a system (or sensor) "wants" to stay in the same state as it was. It basically allows conditions around a system to change to some extent without causing the system in question to respond as it normally would. A heating or cooling system's thermostat, for example, employs hysteresis  so that the room temperature can change slightly without the attached heating or cooling system being continually triggered over minute changes in temperature.

In the case of your SRT5KRMXLI UPS, enabling the Hysteresis  setting would allow the temperature setting to "swing" a little more than it normally would before an alarm is triggered to indicate a problem or warning. You can set how much "swing" over the upper or lower limits is allowed.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

0 Likes
0
3389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

The way I like to think about it is that without hysteresis, if the threshold is 50 degrees and the temperature is at 50 degrees, the recorded temperature will move a little above and below 50 degrees repeatedly triggering and clearing the temperature alarm as it drifts despite the temperature not actually changing much. That's a nuisance. Instead with hysteresis we have two thresholds: one that triggers the alarm, and another one (offset by the hysteresis amount) that clears the alarm. The temperature can drift all it wants between these two thresholds without causing nuisance alarm activity.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

0 Likes
0
3389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

Thanks William. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

0 Likes
0
3390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:37 AM . Last Modified: ‎2024-03-13 04:36 AM

Thanks Voidstar.

Reply

Link copied. Please paste this link to share this article on your social media post.

BarcodeMaker
BarcodeMaker
Cadet

Posted: ‎2023-01-19 12:45 AM

0 Likes
0
2893
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-19 12:45 AM

Hysteresis  control a cooling or heating element at the appropriate threshold.

Reply

Link copied. Please paste this link to share this article on your social media post.

TradeLabelSoftware
TradeLabelSoftware
Cadet

Posted: ‎2023-01-19 03:07 AM

0 Likes
0
2887
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-19 03:07 AM

Hysteresis is a property of the behavior of magnetic materials. The hysteresis pattern is a common pattern.

DRPU Trade Label Software by https://www.tradelabelsoftware.com
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore