HELP! Forgot password for AP9617 NICs in Smart-UPS 2200XLs

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • HELP! Forgot password for AP9617 NICs in Smart-UPS 2200XLs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:45 AM . Last Modified: ‎2024-03-07 02:37 AM

0 Likes
3
1342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:45 AM . Last Modified: ‎2024-03-07 02:37 AM

HELP! Forgot password for AP9617 NICs in Smart-UPS 2200XLs

Hi,

I have 30 UPSs installed in various secure remote locations. Three weeks ago I changed the password for the apc account to something more secure on all 30 UPSs. I made note of the new non-trivial password in our password database which has since become corrupt. I cannot remember what I changed the password to.

Is there a backdoor which would allow me to get in and reset the password for the apc account?
Is there a way to find out what I set the password to? I can get console access to 2 of the UPSs and I used the same password for all 30 so if I can get into 1 I will be able to get into all 30.
I have setup InfraStraXure Central Basic with SNMPv3 monitoring of all 30 UPSs. Is there anyway I can use this software to change the password via SNMP or anything else?

Please help. Thanks, Ian.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:45 AM . Last Modified: ‎2024-03-07 02:37 AM

0 Likes
0
1341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:45 AM . Last Modified: ‎2024-03-07 02:37 AM

Hi,

I was able to change the password to the apc account on all 30 UPSs using SNMPv3 from the ISX applicance to each UPS!

Thank god I setup SNMP correctly ... it saved my bacon.

Ian.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-30 08:45 AM . Last Modified: ‎2024-03-07 02:37 AM

0 Likes
0
1341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:45 AM . Last Modified: ‎2024-03-07 02:37 AM

Ian,

I kindly request you to call in the APC Customer Care Center at 1-800-800-4272 or http://www.apc.com/support/index.cfm as they can provide you the back door password of your NMC card.

You may view the below K-base document which explains the the password recovery procedure on the NMC.
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=8091

I do not think that you can recover the password which you had set before even if you get the back door password.

I hope that it helps.

Message was edited by: Techie

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:45 AM . Last Modified: ‎2024-03-07 02:37 AM

0 Likes
0
1341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:45 AM . Last Modified: ‎2024-03-07 02:37 AM

yes, techie is right. you can only reset the password if you do not know it using the knowledgebase article he provided. there is no backdoor password on this card and you also will not be able to see what the password is currently set to, only reset it to a username/password of apc/apc.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:45 AM . Last Modified: ‎2024-03-07 02:37 AM

0 Likes
0
1342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:45 AM . Last Modified: ‎2024-03-07 02:37 AM

Hi,

I was able to change the password to the apc account on all 30 UPSs using SNMPv3 from the ISX applicance to each UPS!

Thank god I setup SNMP correctly ... it saved my bacon.

Ian.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore