Group event action notification is not staying disabled

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Group event action notification is not staying disabled
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 08:24 AM . Last Modified: โ€Ž2024-03-07 03:13 AM

0 Likes
6
1373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 08:24 AM . Last Modified: โ€Ž2024-03-07 03:13 AM

Group event action notification is not staying disabled

Hello -

I have a frustrating issue I'm hoping someone can help me resolve.

Info-
Model: Smart-UPS 700 RM
Firmware Revision: 52.11.D

My workflow:

Administration>Notification>Event Actions by Group

Select 'Events by Severity' radial

and then Check 'Informational' only.

Next

Select 'Email Recipients' Radial

Next

select top two email addresses "XXX@XX.com" and "XXY@XX.com"

Next

Select Radial next to 'Disable Notifications'

Next

Confirm and Apply

I then get a screen that tells me "Actions have been successfully applied." and allows me to click 'Finish'

I've seemingly disabled those notifications, however, when I go back and check, they're enabled again.

What am I doing wrong?

Thanks much for any assistance you can render!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-30 08:24 AM . Last Modified: โ€Ž2024-03-07 03:08 AM

0 Likes
0
1373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 08:24 AM . Last Modified: โ€Ž2024-03-07 03:08 AM

under (Event Action Config), yes, there should be more - you should see ALL of the events the NMC is able to send/report in the event log to you about the UPS and network management card itself. that is strange.

i forgot what you had said prior and you only want to disable informational events but still want to get all the warning and critical events. sorry about that.

i would suggest downloading that config.ini, delete the entire (event action config) section (and also maybe remove the (NetworkEMAIL section just incase theres something funny going on with that) out of the bottom of it, and save it on your computer. then go to the card and go to Administration->General->Reset/Reboot and reset the card to defaults EXCEPT or EXCLUDING TCP/IP. then configure the notifications and disable ALL informational, warning, and critical. test the self test to see if you get it. if not, then go back and ENABLE notifications for only critical and warning the way that you want them. then go to Administration->General->user config file and browse for that config.ini you edited so it will upload all the rest of the settings you had for the other areas of the card. alternatively, you could reconfigure it all over again if you wanted.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-30 08:24 AM . Last Modified: โ€Ž2024-03-07 03:13 AM

0 Likes
0
1373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 08:24 AM . Last Modified: โ€Ž2024-03-07 03:13 AM

when you are going back to the initial configure by group screen, the radio button just defaults back to "Enable Notifications" even though they arent enabled. As long as you got the message that settings were successfully applied, they should be. I tried it myself to make sure and confirm my belief.

What we can do is go through and disable the notifications and apply the settings, then you can check the config.ini file on the card and make sure notifications arent enabled for the events you disabled. You can view config.ini through ftp:// or you can open FTP session directly with the card and download the file config.ini and look at the bottom of it.

FYI, when the events are NOT configured for notifications, it should look similar to this (you will see brackets like this '[' and ']' but the HTML coding of the forum translates them to links):

; UPS: The output power is now turned off.
E0114=ES,E[-:::],T[:::::],P[+:+:+:+]

when event notifications are enabled, it will look something like this (I have notifications enabled to repeat every two minutes until the condition clears)

; UPS: The output power is turned off.
E0114=ES,E[--05S+02M-1:::],T[:::::],P[:::]

The E before the brackets are the email configuration, the T is for SNMP traps and P is for paging (even if you dont have an NMC with paging you should see this).

hope this answers your question!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 08:24 AM . Last Modified: โ€Ž2024-03-07 03:08 AM

0 Likes
0
1373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 08:24 AM . Last Modified: โ€Ž2024-03-07 03:08 AM

Thanks for the great reply!


I also neglected to mention that when I did disable the notifications, (this is stemming from the bi-monthly self-test) we still got the self-test, that was my first clue that my attempt to disable the notification didn't work. I tried it again yesterday and then tested by initializing a self-test - sure enough, the notification came through (even though I disabled it yet again)

Well, I did what you tried and took a look at the config.ini.. I'm guessing I should see more EventActionConfig entries than I do.. See below for the entire section (pasted it here)

Is there something flaky going on with this config.ini? The fact that the entry doesn't appear to be there might be a reason why the setting isn't sticking?

[EventActionConfig]

; Environment: A fault no longer exists for integrated Environmental Monitor Output Relay ({name} at {location}).
E0326=ES,E[:::],T[:::::],P[+:+:+:+]

; Environment: A warning fault exists for external Environmental Monitor input contact 1 ({name} at {location}).
E033F=ES,E[--05S+02M-1:--05S+02M-1:+-05S+03M-1:+-05S+03M-1],T[:::::],P[:::]

; Environment: A warning fault exists for external Environmental Monitor input contact 2 ({name} at {location}).
E0340=ES,E[--05S+02M-1:--05S+02M-1:+-05S+03M-1:+-05S+03M-1],T[:::::],P[:::]

; Environment: A warning fault exists for external Environmental Monitor input contact 3 ({name} at {location}).
E0341=ES,E[--05S+02M-1:--05S+02M-1:+-05S+03M-1:+-05S+03M-1],T[:::::],P[:::]

; Environment: A warning fault exists for external Environmental Monitor input contact 4 ({name} at {location}).
E0342=ES,E[--05S+02M-1:--05S+02M-1:+-05S+03M-1:+-05S+03M-1],T[:::::],P[:::]

; Environment: A warning fault exists for integrated Environmental Monitor input contact {number} ({name} at {location}).
E0343=ES,E[--05S+02M-1:--05S+02M-1:+-05S+03M-1:+-05S+03M-1],T[:::::],P[:::]

; Environment: Restored the local network management interface-to-integrated Environmental Monitor Input sensor ({name} at {location}) communication.
E0344=ES,E[:::],T[:::::],P[+:+:+:+]

; Environment: Lost the local network management interface-to-integrated Environmental Monitor Input sensor ({name} at {location}) communication.
E0345=ES,E[+-05S+03M-1:+-05S+03M-1:+-05S+03M-1:+-05S+03M-1],T[:::::],P[:::]

; Environment: Restored the local network management interface-to-external Environmental Monitor sensor {number} ({name} at {location}) communication.
E0346=ES,E[:::],T[:::::],P[+:+:+:+]

; Environment: Lost the local network management interface-to-external Environmental Monitor sensor {number} ({name} at {location}) communication.
E0347=ES,E[+-05S+03M-1:+-05S+03M-1:+-05S+03M-1:+-05S+03M-1],T[:::::],P[:::]

; Environment: Restored the local network management interface-to-external Environmental Monitor input contact {number} ({name} at {location}) communication.
E0348=ES,E[:::],T[:::::],P[+:+:+:+]

; Environment: Lost the local network management interface-to-external Environmental Monitor input contact {number} ({name} at {location}) communication.
E0349=ES,E[+-05S+03M-1:+-05S+03M-1:+-05S+03M-1:+-05S+03M-1],T[:::::],P[:::]

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-30 08:24 AM . Last Modified: โ€Ž2024-03-07 03:08 AM

0 Likes
0
1373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 08:24 AM . Last Modified: โ€Ž2024-03-07 03:08 AM

hm yes it doesnt look like the settings are getting set in the config.ini since you can still see the numbers after the E for email.

to confirm you should be doing the following:

Logging and going to Administration->Notification->Events (on the left hand side)->By Group->Events by Severity (with Information, Warning and Critical all selected)->Push Next->Choose the radio button for Email recipients->Push Next->Select your email recipient->Push Next->Select the radio button for Disable Notifications->Push Next->Confirm the following screen says "Define event actions for these groups: Severity: Informational, Warning, Critical | When the event condition occurs, the following recipients will not be notified: email@yourdomain.com." ->Push apply->Confirm you receive the message that says "Actions have been successfully applied."

i believe you are doing this correctly but I just want to confirm. If not, try the above steps. I did it as I typed it out so there should be no errors ๐Ÿ˜‰

if this still doesnt work, i'd download the config.ini via FTP so you have a copy then try resetting the card to defaults excep TCP/IP and going through the steps above to see what happens. then we can delete the event configuration off of the config.ini card and then upload the rest of the config.ini to the card under the Administration->General->User config file option so that the rest of your settings besides the event notification will be copied back over to the card. i can clarify that further if you need it when we get to that step.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 08:24 AM . Last Modified: โ€Ž2024-03-07 03:08 AM

0 Likes
0
1373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 08:24 AM . Last Modified: โ€Ž2024-03-07 03:08 AM

Thanks much, I picked a winna -

The only difference between what you described and what I did is I only selected 'Informational Events' and not all as you had mentioned.

Also - should there be more entries in the event actions config section of the config.ini than what I listed? I only count 9 entries.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-30 08:24 AM . Last Modified: โ€Ž2024-03-07 03:08 AM

0 Likes
0
1374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 08:24 AM . Last Modified: โ€Ž2024-03-07 03:08 AM

under (Event Action Config), yes, there should be more - you should see ALL of the events the NMC is able to send/report in the event log to you about the UPS and network management card itself. that is strange.

i forgot what you had said prior and you only want to disable informational events but still want to get all the warning and critical events. sorry about that.

i would suggest downloading that config.ini, delete the entire (event action config) section (and also maybe remove the (NetworkEMAIL section just incase theres something funny going on with that) out of the bottom of it, and save it on your computer. then go to the card and go to Administration->General->Reset/Reboot and reset the card to defaults EXCEPT or EXCLUDING TCP/IP. then configure the notifications and disable ALL informational, warning, and critical. test the self test to see if you get it. if not, then go back and ENABLE notifications for only critical and warning the way that you want them. then go to Administration->General->user config file and browse for that config.ini you edited so it will upload all the rest of the settings you had for the other areas of the card. alternatively, you could reconfigure it all over again if you wanted.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 08:24 AM . Last Modified: โ€Ž2024-03-07 03:08 AM

0 Likes
0
1373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 08:24 AM . Last Modified: โ€Ž2024-03-07 03:08 AM

Thanks I picked a winna - I reset all settings and reconfigured the UPS.. works fine now.

Much thanks for your help!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of