Getting error messages about power or frequency with a SRT5KRMXLT

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Getting error messages about power or frequency with a SRT5KRMXLT
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:44 AM . Last Modified: ‎2024-03-15 06:13 AM

0 Likes
4
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:44 AM . Last Modified: ‎2024-03-15 06:13 AM

Getting error messages about power or frequency with a SRT5KRMXLT

The error messages I am getting are:

02/06/2019 07:36:10 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.
02/06/2019 07:36:08 UPS: Bypass not in range ; either frequency or voltage.
02/06/2019 07:36:08 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.
02/06/2019 07:36:07 UPS: Bypass not in range ; either frequency or voltage.
02/06/2019 07:36:07 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.

and I have been graphing the voltage and frequency since it has been installed. The input voltage is between 235.51 and 248.52, and the frequency is 59.28 and 61. Both the voltages and frequency are well within the tolerances of:

Input voltage range for main operations            160 - 275V

Input frequency                                              40 - 70 Hz (auto sensing)

Anybody have any ideas? Is this something I should be worried about?

Thanks! 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:44 AM . Last Modified: ‎2024-03-15 06:13 AM

0 Likes
0
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:44 AM . Last Modified: ‎2024-03-15 06:13 AM

Hi Liam

I did find that setting, and changed it on one UPS, and that seems to have fixed the problem. I have changed the other, and will monitor over the weekend, but I think this is the fix. Thanks for your help.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:44 AM . Last Modified: ‎2024-03-15 06:13 AM

0 Likes
0
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:44 AM . Last Modified: ‎2024-03-15 06:13 AM

Hi Ross - 

The tolerances you mentioned are in regards to when the UPS will function online. The issue you are seeing is not that the UPS is on battery, but that the UPS is telling you it would not go to bypass due to the current input power. To configure this you would go to the web interface of the Network Management Card and Click on "Configuration", then "Power Settings". From there you can configure the power parameters for Bypass Operation. 

Thank

Liam 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:44 AM . Last Modified: ‎2024-03-15 06:13 AM

0 Likes
0
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:44 AM . Last Modified: ‎2024-03-15 06:13 AM

Thanks for the response Liam. I did that when I first configured the UPS, and the values that I used was 250V for upper limit, and 160V for the lower. The Output Upper/Lower values are 220/184 so everything should be correct, and because of the errors, the project might be put on hold until things are corrected. Is there anywhere else I should be looking?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:44 AM . Last Modified: ‎2024-03-15 06:13 AM

0 Likes
0
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:44 AM . Last Modified: ‎2024-03-15 06:13 AM

Hi Ross - 

Try setting the Output frequency range to 60Hz +/- 3.0 and the transfer mode  to "Phase Lock Not Required"

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:44 AM . Last Modified: ‎2024-03-15 06:13 AM

0 Likes
0
1625
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:44 AM . Last Modified: ‎2024-03-15 06:13 AM

Hi Liam

I did find that setting, and changed it on one UPS, and that seems to have fixed the problem. I have changed the other, and will monitor over the weekend, but I think this is the fix. Thanks for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of