Hi,
I just got my AP7911B switched PDU.
The wattage provided by the colocation for my rack is 30A with 208v, and my devices are using total of ~4.9kw.
Each device takes about 3A, there are 8 devices, thus the total currents I am using are 24A, and sometimes it can go over a bit by %7.
That said, I am getting the Phase1 Load Critical Warning quite often. Looks like APC PDU enforces the 80% rule of derated input currents.
My questions are how safe/unsafe is it to ignore these warnings ? At what amps will it actually hit the circuit breaker?
If I know for sure that my devices won't take more than 27 amps in total (90% of actualy max capacity), is it safe to operate at this level ?
Thank you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-10 01:22 AM . Last Modified: 2021-07-10 01:24 AM
To specify the phase to be used, add the “|” delimiter to one (and only one) of the input key strings followed by one of the phase strings in the table below: On each call to PropsSI (), the imposed phase is reset to “not_imposed” as long as no imposed phase strings are used.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-10 01:22 AM . Last Modified: 2021-07-10 01:24 AM
To specify the phase to be used, add the “|” delimiter to one (and only one) of the input key strings followed by one of the phase strings in the table below: On each call to PropsSI (), the imposed phase is reset to “not_imposed” as long as no imposed phase strings are used.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.