Hi,
This is probably such a basic question but I'm very new to power and Backup.
is it possible to use a PDU without a UPS? I.E. Plugged straight into the mains?
I'm interested in using the features of a metered UPS (outlet power up down, load monitoring etc) but don't need battery backup.
Can I literally get a C20 -> Mains cable can plug the PDU directly into the mains or does the PDU require a UPS in order to function?
Thanks,
Tom
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-10 04:06 PM . Last Modified: 2021-07-10 04:24 PM
Sometimes you find a solution to a problem with a unconventional approach !!!!
In our neighborhood the 3 phase power wires powering the stepdown transformer which feed our building are aerial with a very close tree branch and quite often we have serious problems with squirrels jumping on the wires, unfortunately they die when touching two of the wires forcing any of the 3 protective fuses to blow and leaving us with any of the three phases down. It could take several hours before the power company came to replace the blown fuse so I installed a ATS / metered PDU ( on my case a UPS and some other critical devices are plugged on it but this is only an example ) and hooked the primary ATS / PDU input to one phase AC input and the secondary input plugged to another phase. With this solution we have always power feeding this ATS / metered PDU no matter which phase is down until the power company fix it. And of course if I am out of the house I receive a message notification about the problem of the phase down.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:47 AM . Last Modified: 2024-01-31 03:02 AM
Hi Thomas,
A PDU can be used as a stand-alone device. It does not need a UPS to function. As long as the power requirements are met, then it should work. A UPS is typically recommended to clean incoming power or to avoid possible surges passing to your loads, as a PDU does not have surge protection.
You may check the PDU selector here: http://www.apc.com/us/en/tools/selector/pdu/index.cfm?ISOCountryCode=us
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:47 AM . Last Modified: 2024-02-14 10:14 PM
Brilliant thanks Mike, I'd not considered surges, although the facility is using a central "big" UPS so this is probably catered for there.
Kind Regards,
Tom
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-10 04:06 PM . Last Modified: 2021-07-10 04:24 PM
Sometimes you find a solution to a problem with a unconventional approach !!!!
In our neighborhood the 3 phase power wires powering the stepdown transformer which feed our building are aerial with a very close tree branch and quite often we have serious problems with squirrels jumping on the wires, unfortunately they die when touching two of the wires forcing any of the 3 protective fuses to blow and leaving us with any of the three phases down. It could take several hours before the power company came to replace the blown fuse so I installed a ATS / metered PDU ( on my case a UPS and some other critical devices are plugged on it but this is only an example ) and hooked the primary ATS / PDU input to one phase AC input and the secondary input plugged to another phase. With this solution we have always power feeding this ATS / metered PDU no matter which phase is down until the power company fix it. And of course if I am out of the house I receive a message notification about the problem of the phase down.