GFI trips

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • GFI trips
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:37 PM . Last Modified: ‎2024-03-15 03:53 AM

0 Likes
6
910
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:37 PM . Last Modified: ‎2024-03-15 03:53 AM

GFI trips

Hi all,

Great forum and of course APC what more can one say!

In one client location I have a Symmetra RM 6000 running well.

We tried a Residual Current Detector [GFI] on the output to comply with the wiring code and it lasted three days before tripping one morning as the load isolator timed the network on.

It keeps tripping on one part of the load and I will be onsite in a few hours to do some digging around.

Is it likely to be the common mode switching currents from the RM 6000 which is doing this?

Would we be ok to de commission it and install a line interactive unit, although they aren't large enough to really cope unless say two RM 3000's would be ok perhaps.

Thanks.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:37 PM . Last Modified: ‎2024-03-15 03:53 AM

0 Likes
0
907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:37 PM . Last Modified: ‎2024-03-15 03:53 AM

Computers normally have a few mA of leakage current to the ground, because each side of the line is capacitively coupled to the ground.

Each computer's front end has a filter that's setup like this:

L--||--G--||--N
together with a pair of series reactors between the rest of the power supply and a capacitor that goes directly between L and N. Since computer power supplies are designed for global use, they pretty much all have the same design.

This common front end is designed to keep high frequency noise from getting into the mains and will inherently have some leakage current, therefore, you should have all IT loads connected to a grounded circuit and not with a GFCI.

I'm not sure about the code in Australia, but here in the US, permanently installed (i.e. refrigerators, computers, appliances) grounded fixtures are not used with GFCIs.

This is something you need to consult your an electrician or an inspector familiar with AUSTRALIAN codes.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:37 PM . Last Modified: ‎2024-03-15 03:53 AM

0 Likes
0
908
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:37 PM . Last Modified: ‎2024-03-15 03:53 AM

Computers normally have a few mA of leakage current to the ground, because each side of the line is capacitively coupled to the ground.

Each computer's front end has a filter that's setup like this:

L--||--G--||--N
together with a pair of series reactors between the rest of the power supply and a capacitor that goes directly between L and N. Since computer power supplies are designed for global use, they pretty much all have the same design.

This common front end is designed to keep high frequency noise from getting into the mains and will inherently have some leakage current, therefore, you should have all IT loads connected to a grounded circuit and not with a GFCI.

I'm not sure about the code in Australia, but here in the US, permanently installed (i.e. refrigerators, computers, appliances) grounded fixtures are not used with GFCIs.

This is something you need to consult your an electrician or an inspector familiar with AUSTRALIAN codes.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:37 PM . Last Modified: ‎2024-03-15 03:53 AM

0 Likes
0
907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:37 PM . Last Modified: ‎2024-03-15 03:53 AM

Thank you for the reply, it is appreciated.

I have swapped in a LI APC ups and the fault tripping went away when it was endemic just prior.

I remember a conversation with the APC support channel engineer who said that the input to a Symmetra would cause nuisance tripping as is the case due to the MOV's / Varistors & common mode filters present along with the dual conversion process.

Apparently where the Symmetra is concerned so does the output!

The engineer reported:

Now to answer your question, it is not recommended to connect a ELCB on the input side of your UPS as it will cause nuisance tripping due to leakage currents caused by the UPS. These leakage currents are generated by MOV's and other electronic components inside the UPS which will result in tripping of your ELCB if connected on the input side.

You can place the ELCB on the output side instead and provide protection for people working with your equipments.

Actually my support channel lead me back to this online help link:

http://jpaa-en.apc.com/cgi-bin/jpaa_en.cfg/php/enduser/std_adp.php?p_faqid=1344&p_created=1010390400...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-15 03:53 AM

0 Likes
0
907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-15 03:53 AM

I found this reference to an "LI APC UPS" in http://forums.isxusergroups.com/message.jspa?messageID=1917
I wonder if I could get some more details about the LI APC ups. Is LI a model indicator or a reference to a certain technology?? Thanks


"I have swapped in a LI APC ups and the fault tripping went away when it was endemic just prior. "

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-15 03:53 AM

0 Likes
0
907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-15 03:53 AM

Steve,

My apologies as you should also have an email from me in your inbox for submitting an Answer Feedback for an APC Knowledge Base. Please close the other incident with Email Support, as I am their escalation point so it may be easier to interface w/ me directly. Here's the response that I provided in the email:

Coincidentally enough, I am also the APC Forums Admin who was in the process of contacting our Back-UPS engineers before providing a response. I noticed in your initial question that you asked for more information pertaining to the LI APC UPS. From the information I've received, LI stands for Line-Interactive, which is one of the primary UPS Topologies that we use. The XS1500 that you have is a Line Interactive UPS, as well as all of our Smart-UPS models that are not Smart-UPS RT, VT or Modular. Is there anything in particular that's occurring with the system that's raising an eyebrow to the GFCI?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-15 03:53 AM

0 Likes
0
907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-15 03:53 AM

I have an APC XS1000 UPS which is powering an HP XW 4400 workstation in an industrial
application. The UPS and in turn the HP workstation are powered via a
GFCI-protected circuit. My problem is that the GFCI trips each time the
HP XW 4400 is turned on. I have tried this with several different XW
4400 workstation units with the same result.
The GFCI trips with or without the UPS in circuit.
If I use an HP 5150 model PC instead of the XW 4400 the GFCI does not trip
If I unplug the UPS prior to powering the workstation ON I can then plug in the UPS and carry on without problem.

My question is essentially this. Is there an APC product which would
provide backup power to the computer while at the same time eliminating
the tripping of the GFCI?

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-15 03:53 AM

0 Likes
0
907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:38 PM . Last Modified: ‎2024-03-15 03:53 AM

Do you have the inrush current of this machine? It seems to be extremely excessive to the point where it's exceeding 15A to trip the GFCI. You may have to look at a larger, double-conversion online UPS. Those would be the Smart-UPS RT or possibly a smaller scale Symmetra LX.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of