Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
Float voltage fluctuating but mostly too low
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-2307:44 AM
Float voltage fluctuating but mostly too low
We have some 70+ APC Smart-UPS SMT1000RM2U units deployed at small wireless repeater sites. They are monitored via AP9630 management cards. Typically, the battery voltage reported by SNMP is 27.0 volts which seems correct for floating 24 volts of sealed lead acid cells.
However, we now have several sites where the reported battery voltage is much lower most of the time, going up approximately once every week to 27.0 volts for 24-30 hours and then back down for the rest of the interval. I've attached a SNMP record for the last month at one such site.
We recently had a commercial power outage while the battery voltage was reported as 26.0v and indeed, during the power outage, the battery voltage declined much more rapidly than I would have expected had the batteries been correctly floated at 27.0v.