Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Firmware for my ap9606

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: Firmware for my ap9606
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:02 AM . Last Modified: ‎2024-03-13 11:32 PM

0 Likes
17
4463
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:02 AM . Last Modified: ‎2024-03-13 11:32 PM

Firmware for my ap9606

I recently purchased a used ap9606 network management card for my Smart-UPS 1500. It probably needs a firmware upgrade but I can't seem to find firmware for this older model. Also, I get the error "MasterSwitch : Wrong Application Loaded for Attached Device" when I connect to the card. I want to use this with Powerchute Network Shutdown (I think?) but the software cannot seem to locate my card. I don't think its a network issue since I can talk to card via HTTP and SSH. I think all these problems are due to having the wrong software on my ap9606 since I don't use the MasterSwitch product. I've been poking around the internet looking for a solution.

Any ideas?
Thanks

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
brian163_apc
Crewman brian163_apc
Crewman

Posted: ‎2021-06-29 01:03 AM . Last Modified: ‎2024-03-13 11:32 PM

0 Likes
3
4464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:03 AM . Last Modified: ‎2024-03-13 11:32 PM

On 5/8/2016 3:14 PM, John said:

Indeed. I too am still using an AP9606 and needed to upgrade the firmware. For posterity:

I was able to upgrade the firmware from my Mac using command-line ftp (note that the "hash" command is optional, and the "passive" command was needed to disable passive mode):

ftp> bin

ftp> hash

ftp> passive

ftp> put aos326b.bin

ftp> quit

I'm working on a 19 year old APC SU1400NET from a Mac and I appreciate everyone's effort to pay it forward in this thread. For my part, note that after upgrading the AOS (OS &TCP/IP Stack) as John stated, you may also have to update the built in APP. In my case this was the sumx326.bin file:

ftp> bin

ftp> hash

ftp> passive

ftp> put sumx326.bin

ftp> quit

May these units run forever! laughing cool

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 17
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:02 AM . Last Modified: ‎2024-03-13 11:32 PM

0 Likes
0
4456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:02 AM . Last Modified: ‎2024-03-13 11:32 PM

Thanks for sharing the information with us.

  • Tags:
  • ap9606
  • apc
  • card
  • management
  • masterswitch
  • network
  • PowerChute
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:02 AM . Last Modified: ‎2024-03-13 11:32 PM

0 Likes
0
4456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:02 AM . Last Modified: ‎2024-03-13 11:32 PM

I reseated the card, and tried ftp with the command has added. I still get the same error, but with a line of ############## after the 150 message. Also, once this happens if i try reconnecting with ftp it just says "connected to 192.168.20.31" and just sits there until i hit the reset button on the management card

Message was edited by: businesscomputerdesign

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:02 AM . Last Modified: ‎2024-03-13 11:32 PM

0 Likes
0
4455
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:02 AM . Last Modified: ‎2024-03-13 11:32 PM

I recently purchased a used ap9606 network management card for my Smart-UPS 1500. It probably needs a firmware upgrade but I can't seem to find firmware for this older model. Also, I get the error "MasterSwitch : Wrong Application Loaded for Attached Device" when I connect to the card. I want to use this with Powerchute Network Shutdown (I think?) but the software cannot seem to locate my card. I don't think its a network issue since I can talk to card via HTTP and SSH. I think all these problems are due to having the wrong software on my ap9606 since I don't use the MasterSwitch product. I've been poking around the internet looking for a solution.

Any ideas?
Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:02 AM . Last Modified: ‎2024-03-13 11:32 PM

0 Likes
0
4455
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:02 AM . Last Modified: ‎2024-03-13 11:32 PM

I used the bin command, and the guide didn't say anything about hash. I've tried to push it via command-line ftp, and I also tried to pull the file via Telnet from a Filezilla ftp server, both seem to fail. I'll try reseating the card right now..

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:02 AM . Last Modified: ‎2024-03-13 11:32 PM

0 Likes
0
4455
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:02 AM . Last Modified: ‎2024-03-13 11:32 PM

Thank You so much for finding the firmware for me. I am having issues installing it via FTP though. i get this:

after:
ftp> put aos326b.bin
200 command okay.
150 opening data connection for aos326b.bin

i get:

Netout :Connection reset by peer
Connection closed by remote host
ftp
If i try and reconnect:
C:\apc ftp 192.168.20.31
Connected to 192.168.20.31

Connection Closed by remote host.

Am I doing something wrong?

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:02 AM . Last Modified: ‎2024-03-13 11:32 PM

0 Likes
0
4455
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:02 AM . Last Modified: ‎2024-03-13 11:32 PM

did you do the commands of bin and hash first? is the AOS the first file you put on there? you didnt put the APP first, correct?

also, can you try to reseat the card in the UPS? just pull it out for 5-10 seconds, then reinsert and try again.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:02 AM . Last Modified: ‎2024-03-13 11:32 PM

0 Likes
0
4455
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:02 AM . Last Modified: ‎2024-03-13 11:32 PM

hmm. what firmware is on it now? if you web or telnet it in will indicate it in the interface.i just know that you mentioned it was a masterswitch firmware.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:03 AM . Last Modified: ‎2024-03-13 11:32 PM

0 Likes
0
4455
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:03 AM . Last Modified: ‎2024-03-13 11:32 PM

You can use the update utitlity for the AP96117 cards. Just place the two bin files for the 9606 cards into the same directory you unzipped the 9617 utility into. Then change the text of the config.txt to:
AOS = aos325.bin
APP = sumx326.bin


Works just fine.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:03 AM . Last Modified: ‎2024-03-13 11:32 PM

0 Likes
0
4455
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:03 AM . Last Modified: ‎2024-03-13 11:32 PM

Hi, where do you find the utility that you mentioned? Also, the link to the knowledge base article that "winna" mentioned in her earlier post seems dead. Thanks in advance!

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:03 AM . Last Modified: ‎2024-03-13 11:32 PM

0 Likes
0
4455
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:03 AM . Last Modified: ‎2024-03-13 11:32 PM

yes, that is the issue most likely.

here is a link to the latest firmware:

ftp://ftp.apc.com/apc/public/hardware/webcard/firmware/security/v326b/

for Smart UPS, download the AOS file and the sumx file. then follow the instructions in [this knowledgebase|http://nam-en.apc.com/app/answers/detail/a_id/768] to upgrade via manual FTP.

keep in mind, AP9606 is 10+ years old so it is not currently being tested with the last versions of powerchute. it should still work though so give it a try after you upgrade the firmware.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:03 AM . Last Modified: ‎2024-03-13 11:32 PM

0 Likes
0
4455
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:03 AM . Last Modified: ‎2024-03-13 11:32 PM

On 12/6/2013 3:35 PM, Miles said:

I know that this is an old thread, but this page was the first result returned by Google when I searched for AP9606 firmware upgrade. Therefore, I'm posting the following to aid others who are still using the AP9606 card.

Indeed. I too am still using an AP9606 and needed to upgrade the firmware. For posterity:

I was able to upgrade the firmware from my Mac using command-line ftp (note that the "hash" command is optional, and the "passive" command was needed to disable passive mode):

ftp> bin

ftp> hash

ftp> passive

ftp> put aos326b.bin

ftp> quit

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
brian163_apc
Crewman brian163_apc
Crewman

Posted: ‎2021-06-29 01:03 AM . Last Modified: ‎2024-03-13 11:32 PM

0 Likes
3
4465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:03 AM . Last Modified: ‎2024-03-13 11:32 PM

On 5/8/2016 3:14 PM, John said:

Indeed. I too am still using an AP9606 and needed to upgrade the firmware. For posterity:

I was able to upgrade the firmware from my Mac using command-line ftp (note that the "hash" command is optional, and the "passive" command was needed to disable passive mode):

ftp> bin

ftp> hash

ftp> passive

ftp> put aos326b.bin

ftp> quit

I'm working on a 19 year old APC SU1400NET from a Mac and I appreciate everyone's effort to pay it forward in this thread. For my part, note that after upgrading the AOS (OS &TCP/IP Stack) as John stated, you may also have to update the built in APP. In my case this was the sumx326.bin file:

ftp> bin

ftp> hash

ftp> passive

ftp> put sumx326.bin

ftp> quit

May these units run forever! laughing cool

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
kevindd992002
Crewman kevindd992002
Crewman

Posted: ‎2022-05-26 09:01 AM

In response to brian163_apc
0 Likes
2
3875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-26 09:01 AM

I'm having problems updating the firmware of my ap9606. I'm stuck here for some reason:

 

kevindd992002@Alvin-Desktop:~$ cd /mnt/c/temp
kevindd992002@Alvin-Desktop:/mnt/c/temp$ ls
Spiderman.No.Way.Home.2021.2160p.UHD.BluRay.REMUX.HDR.HEVC.ATMOS-RU4HD.nzb aos326b.bin sumx326a.bin
kevindd992002@Alvin-Desktop:/mnt/c/temp$ ftp 192.168.55.74
Connected to 192.168.55.74.
220 AP9619 Network Management Card AOS v2.6.4 FTP server ready.
Name (192.168.55.74:kevindd992002): apc
331 User name okay, need password.
Password:
230 User logged in, proceed.
ftp> bin
200 TYPE Command okay.
ftp> hash
Hash mark printing on (1024 bytes/hash mark).
ftp> passive
Passive mode on.
ftp> passive
Passive mode off.
ftp> put aos326b.bin
local: aos326b.bin remote: aos326b.bin
200 PORT Command okay.
150 File status okay; about to open data connection.

 

I also tried curl and it just doesn't work:

 

root@UC-CK:/tmp# curl -T aos326b.bin --ftp-port - ftp://192.168.55.74 --user apc:apc
% Total % Received % Xferd Average Speed Time Time Time Current
Dload Upload Total Spent Left Speed
0 320k 0 0 0 0 0 0 --:--:-- 0:00:02 --:--:-- 0curl: (55) Send failure: Connection reset by peer

 

Can you please help me out here? Thanks.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
kevindd992002
Crewman kevindd992002
Crewman

Posted: ‎2022-06-04 09:04 AM . Last Modified: ‎2022-06-04 09:05 AM

In response to kevindd992002
0 Likes
1
3720
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-04 09:04 AM . Last Modified: ‎2022-06-04 09:05 AM

C'mon APC people! A little support here please?

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-06-16 10:20 PM

In response to kevindd992002
0 Likes
0
3584
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-16 10:20 PM

Hi @kevindd992002,

 

I just wanted to be sure that what you have is an AP9606, the reason I asked for this is due to the information that you have provided wherein I saw that it was an AP9619.

 

AP9619 Network Management Card AOS v2.6.4 FTP server ready.

 

The AP9619 uses a different firmware that the AP9606, may I know as well if you are using a Mac or Linux OS and if there is a possibility for you to connect serially to the NMC?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
tickerguy
tickerguy
Cadet

Posted: ‎2024-01-23 07:15 PM

0 Likes
0
1751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-23 07:15 PM

I have acquired one of these old cards and I can connect to it, but I can't find the firmware files to update it -- the links above are no longer good.

 

Does anyone knew where they went?

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
tickerguy
tickerguy
Cadet

Posted: ‎2024-01-23 07:19 PM

0 Likes
0
1751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-23 07:19 PM

I too have a 9606 in an older RM1500 which works, but has horribly old firmware (and apparently no SNMP capability, even though the banner says it does.)

 

I can get connected to it and telnet just fine, but the links above for the updated firmware files and instructions on how to send them are expired -- neither link works.  Is there a new location for them?

 

Thanks in advance!

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of