Firmware changes between UPS 03.8/09.2 for SMX1500RMI2U. Attn: APC engineer

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Firmware changes between UPS 03.8/09.2 for SMX1500RMI2U. Attn: APC engineer
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 12:42 AM . Last Modified: ‎2024-03-11 03:42 AM

0 Likes
7
1346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:42 AM . Last Modified: ‎2024-03-11 03:42 AM

Firmware changes between UPS 03.8/09.2 for SMX1500RMI2U. Attn: APC engineer

Can an APC engineer please address my concerns regarding the SMX1500 firmware revisions?

My company has purchased several SMX1500RMI2U and SMX1500RM2U units for use in critical applications. Last year, we purchased one of these units to qualify it for use in our specific application and subjected the unit to EMC, environmental and even seismic testing. This testing was performed on a unit with UPS 03.8 firmware. Unfortunately, when we ordered a new batch of units late last year, some had date code 1211 and some 1234. After speaking at length with "Louie" at APC tech support, I understand that in early 2012 units started shipping with firmware 09.x. He wasn't able to provide much more information about what changed except that the firmware of "newer" units can be upgraded via USB or serial connection, while the "older" units can only be upgraded via serial connection. Also, I was informed that 09.x firmware cannot be downgraded to 03.x.

I suspect there was some internal hardware change to the units that also drove this firmware revision, however Louie wasn't able to confirm this. I would like to hear back from an APC engineer and try to get more details about what specifically changed with the units, both firmware and hardware. Due to the extensive testing that has been performed on the 03.8 unit, we are not able to go back and retest with the 09.2 firmware because the costs would approach $100k. Without know what exactly changed, we aren't able to justify the use of the newer units.

One of the other changes I noticed is differences in how the firmware revisions are reported between 03.8 and 09.2.
In 03.x, the 2nd firmware was called "COM", now it is labeled "MCU"
In 03.x, the 4th firmware was called "CBL", now it is labeled "MBL"

Ideally, I would like to get in touch with the engineering department or a manager in engineering and setup a meeting to discuss the possibility of being able to disclose any additional changes or if internal components were changed.
I can provide a direct email, contact phone number and company name in a non-public message.

Thank you.

Mike

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • firmware
  • smx1500
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:42 AM . Last Modified: ‎2024-03-11 03:41 AM

0 Likes
0
1346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:42 AM . Last Modified: ‎2024-03-11 03:41 AM

ok, i will send you an email. i am not going to be the person that can help much more than i have but i will try to get you set up with someone who can help further.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:42 AM . Last Modified: ‎2024-03-11 03:42 AM

0 Likes
0
1346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:42 AM . Last Modified: ‎2024-03-11 03:42 AM

Have you developed a test procedure for the seismic testing?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:42 AM . Last Modified: ‎2024-03-11 03:41 AM

0 Likes
0
1346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:42 AM . Last Modified: ‎2024-03-11 03:41 AM

is the email in your profile correct and where we'd contact you? we've had to disable private messaging recently due to some issues with it.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:42 AM . Last Modified: ‎2024-03-11 03:41 AM

0 Likes
1
1346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:42 AM . Last Modified: ‎2024-03-11 03:41 AM

hello. what i can tell you now is this:

As far as interoperability (with PowerChute Software or a Network Card), voltage sensitivity, transfer times, transfer points, AVR operation, and efficiency, the updated units perform either identically or very closely to the older units. Electrically, very little changed, the most significant hardware change that comes to mind is the increased trace spacing on the PCB to adhere to an APC design standard, but this does not affect performance.

The FW updates from v03.8 to v09.2 include USB bootloading, additional languages support, and many bugfixes (mostly interoperability bugfixes and UI tweaks).

If we can understand your application better and maybe some more information on the testing you performed, perhaps we can provide more information.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:42 AM . Last Modified: ‎2024-03-11 03:41 AM

0 Likes
0
1346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:42 AM . Last Modified: ‎2024-03-11 03:41 AM

i picKed a winna,

Thank you for the quick response to my question. Can you provide me with a contact email or phone number so we can take this discussion offline? I can then provide you with details regarding my specific application and the testing that was performed. Regarding the changes, our equipment qualification group is VERY conservative with that can and can't be justified on paper without restesting. At one point in the testing, we decided we needed to change the unit sensitivity setting from "REDUCED" to "LOW" and even that required additional retest. My main concern is that electrical design changes to the unit could (and most likely will) affect the unit's electromagnetic susceptibility or emissions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:42 AM . Last Modified: ‎2024-03-11 03:41 AM

0 Likes
0
1346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:42 AM . Last Modified: ‎2024-03-11 03:41 AM

The email in my profile will come to my personal email address. When I tried to register with my work email, our spam filter must have blocked emails your domain. Once I know your email address, I can have your address whitelisted in our spam system so the emails will come through.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:42 AM . Last Modified: ‎2024-03-11 03:41 AM

0 Likes
0
1347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:42 AM . Last Modified: ‎2024-03-11 03:41 AM

ok, i will send you an email. i am not going to be the person that can help much more than i have but i will try to get you set up with someone who can help further.

Reply

Link copied. Please paste this link to share this article on your social media post.

MartinLiska
MartinLiska
Cadet

Posted: ‎2023-03-29 06:39 AM

In response to BillP
0 Likes
0
1028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-29 06:39 AM

hello,

I have a SMX1500RMI2U UPS and need to upgrade firmware. The contemporary firmware download helper from APC/SE doesn't allow me to select SMTSMX20UPS_15-0.enc firmware for download - maybe because my UPS an/or COM firmware(s) are old.

 

Mine:

UPS 03.8

COM 03.8

UBL 05.0

CBL 02.1

 

Sticker at the back of the UPS has this:

SMX1500RMI2U

AS1051122195

 

I don't know what hardware revision it is. I've downloaded one of the older firmwares you've linked to on this forum and flashed (from 3.6 -> 3.8). UBL and CBL parts remained the same.

 

My question is, can I get a link to some older version of firmware for my hardware? I don't know if 3.8 or 9.2 is the latest for this. I feel that the latest APC flasher needs some higher FW revision just to flash the latest official one (UPS 15.0  MCU 10.3  UBL 07.5  MBL 06.0).

 

Using network management card v 2 running v6 firmware, it fails on this:

07/30/2015 04:23:33 Device UPS: Firmware transfer to UPS failed
 07/30/2015 04:23:33 Device UPS: Finished UPS firmware transfer [Xmodem Cancel]
 07/30/2015 04:23:33 Device UPS: Transferring firmware to UPS.
 07/30/2015 04:20:33 Device UPS: Firmware transfer to UPS succeeded.
 07/30/2015 04:20:33 Device UPS: Finished UPS firmware transfer
 07/30/2015 04:15:17 System Web user 'apc' logged out from 10.20.30.123.
 07/30/2015 04:14:01 Device UPS: Transferring firmware to UPS.
 07/30/2015 04:13:18 apc File 'SMTSMX20UPS_15-0.enc' transfer failed.

 

the xmodem abort seems to be the same for flashing over serial cable. I suspect that 3.8 FW is too old to handle the new firmwares (maybe just the size, or encrypted version).

 

Can you please help me to download appropriate older firmware?

FYI: I've read this

https://community.se.com/t5/APC-UPS-Data-Center-Enterprise/APC-UPS-SMX1500-firmware-update-failure-a...

 

Thanks very much in advance,

 

sincerely Martin

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of