Posted: 2025-04-08 02:50 AM . Last Modified: 2025-04-08 02:55 AM
apc>about
E000: Success
Hardware Factory
---------------
Model Number: AP8953
Serial Number: ZA1639008108
Hardware Revision: 02
Manufacture Date: 09/29/2016
MAC Address: 00 C0 B7 FA FF 29
Management Uptime: 0 Days 0 Hours 1 Minute
Network Management Card
---------------
Model Number: AP9538
Serial Number: ZA1639000888
Hardware Revision: 05
Manufacture Date: 09/28/2016
Application Module
---------------
Name: bootmon
Version: v1.0.9
Date: Mar 27 2019
Time: 16:23:06
APC OS(AOS)
---------------
Name: aos
Version: v6.1.3
Date: Nov 15 2013
Time: 10:40:47
APC Boot Monitor
---------------
Name: bootmon
Version: v1.0.9
Date: Mar 27 2019
Time: 16:23:06
apc>
---
I got the app NMC Firmware Update Utility...
Everything was going alright and then randomly it stopped gave error... Now I lost webui control...
"There was a problem loading the application. Please login to the device via telnet for more details."
I also couldn't find anywhere the firmware here.. I needed to use one from a reddit post.
Can someone help me?
I have SSH access still.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-09 12:00 AM
Hello,
First you will need to access the Rpdu console and check the PNA status on CLI as shown below
https://www.se.com/uk/en/faqs/FA156130/
To determine which firmware components are not downloaded properly ,use the latest version 7.1.4 for NMC2 based Rpdu display as shown below
https://www.se.com/us/en/download/document/APC_RPDU2G_714_EN/
you can use FTP or SCP method to manually transfer the corrupted firmware components as explained below
https://www.apc.com/us/en/faqs/FA156047/
and once the firmware files are transferred reboot the NMC and verfiy the PNA status and try to access it again using webUI
Regards,
Karim
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-09 12:00 AM
Hello,
First you will need to access the Rpdu console and check the PNA status on CLI as shown below
https://www.se.com/uk/en/faqs/FA156130/
To determine which firmware components are not downloaded properly ,use the latest version 7.1.4 for NMC2 based Rpdu display as shown below
https://www.se.com/us/en/download/document/APC_RPDU2G_714_EN/
you can use FTP or SCP method to manually transfer the corrupted firmware components as explained below
https://www.apc.com/us/en/faqs/FA156047/
and once the firmware files are transferred reboot the NMC and verfiy the PNA status and try to access it again using webUI
Regards,
Karim
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of