Posted: 2021-06-28 09:31 PM . Last Modified: 2024-03-14 11:51 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:31 PM . Last Modified: 2024-03-14 11:51 PM
Hi all, I'm having some trouble getting the firmware update for an AP9619 management card installed over the network. We have our UPS units attached to a private VLAN to which I connect through tunnelier. While in Tunnelier I can ping, log in and manage the management card fine, but the app doesn't seem to have any proxy settings built in to it. I tried using FreeCap to force it to use my proxy settings, but it still is unable to ping the device. Does anybody know how I can get the firmware over to the device? Thanks for any help.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:31 PM . Last Modified: 2024-03-14 11:51 PM
Use a proxy-capable FTP program. Upload the AOS .bin file. Wait for the card to automatically reboot. Then upload the application .bin file (for example, sumx).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:31 PM . Last Modified: 2024-03-14 11:51 PM
Use a proxy-capable FTP program. Upload the AOS .bin file. Wait for the card to automatically reboot. Then upload the application .bin file (for example, sumx).