Firewall between Powerchute and 9617 ... what ports need to be open?
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
PowerChute Network Shutdown utilizes the following TCP/UDP ports: TCP/UDP 3052 and TCP/UDP 80. PCNS version 2.2.3 utilizes port 6547 for instance 1, 6548 for instance 2, and 6549 for instance 3.
the network management card itself, by default, has FTP and telnet enabled on their default ports as well as the web interface using port 80 for HTTP or 443 for HTTPS.
PowerChute Network Shutdown utilizes the following TCP/UDP ports: TCP/UDP 3052 and TCP/UDP 80. PCNS version 2.2.3 utilizes port 6547 for instance 1, 6548 for instance 2, and 6549 for instance 3.
the network management card itself, by default, has FTP and telnet enabled on their default ports as well as the web interface using port 80 for HTTP or 443 for HTTPS.