New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Error code L.02 and B.02 SMC1500-2UC
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2024-08-2201:46 PM
Error code L.02 and B.02 SMC1500-2UC
I received L.02 and B.02 error codes on my 4 year old SMC1500-2UC. After a hard reboot that entails disconnecting the battery leads the unit restarted and now shows code L.02. Gong into the menu I also found rb.0 with a battery icon with x in the middle. Reply for photo link if needed
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2024-08-2306:47 AM
The battery is end of life - replaced it with a APCRBC132 cartridge. Once the new battery has been installed update the battery installation date.
Doing so will reset the internal counters and adjust the charging lookup tables. Let the new cartridge recharge for at least 24 hours or when the system indicates the battery cartridge is at 100% SOC.
Manually initiate a Self Test and let the system return to 100% SOC. Finally, initiate a battery calibration via the LCD Menu / APC Power Chute software.
Insure there is at least 30% attached load connected to the system. Once complete the operational runtime displayed on the LCD will be more accurate. 👍