Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Enabling SNMP v1 on an NMC installed on a Smart-UPS RT 10000 XL
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3010:20 PM. Last Modified: 2024-03-0611:12 PM
Enabling SNMP v1 on an NMC installed on a Smart-UPS RT 10000 XL
Hello,
I enabled SNMP on the NMC, but cannot get/walk using a SNMP command line client
Seems that SNMP is not enabled since a nmap scan does not show the 161 UDP port open.
Checked everything : community names, IP configuration, gateways, masks. The client and the NMC are on the same subnet.
I wonder if you have to reboot the UPS to enable SNMP.
And if so, will it shutdown power to the loads during the reboot ?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3010:20 PM. Last Modified: 2024-03-0611:12 PM
Hi RodV, you can reboot the NMC (admin -> general -> reset/reboot -> reboot management interface) without having it effect your load (the NMC and the UPS are separate in that fact) however rebooting the ups will take your load down. As for the actually troubleshooting, i would also check to make sure you have the latest powernet MIB installed as well as open ports 161 and 162 UDP. I see you checked the community names, how baout the access type for the community name/s as well. Hope this helps.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3010:20 PM. Last Modified: 2024-03-0611:12 PM
Hi RodV, you can reboot the NMC (admin -> general -> reset/reboot -> reboot management interface) without having it effect your load (the NMC and the UPS are separate in that fact) however rebooting the ups will take your load down. As for the actually troubleshooting, i would also check to make sure you have the latest powernet MIB installed as well as open ports 161 and 162 UDP. I see you checked the community names, how baout the access type for the community name/s as well. Hope this helps.