Email Notifications fail after upgrade to v6.0.6

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Email Notifications fail after upgrade to v6.0.6
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 04:06 AM . Last Modified: ‎2024-03-05 10:26 PM

0 Likes
8
1350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:06 AM . Last Modified: ‎2024-03-05 10:26 PM

Email Notifications fail after upgrade to v6.0.6

I just finished a batch upgrade of AP9630/31s from 5.1.7 to 6.0.6.  After the upgrade I notice I wasn't receiving any email from the UPSs.  I guess the upgrade had reset the smtp server settings.  I didn't think this was too big of a problem because I have a script that can ftp my config.ini to all the UPSs.  However that did not fix the problem.  I figured out that I still have to open the smtp settings page, click apply(don't change any settings, just click apply), then test the email receipt and then everything is good.  I assume this is not normal.  Any workaround to this?  I really don't want to have to do this 159 times.  I also noticed in some cases that if I add a new user via mass ftp'ing the config.ini, I still have to test that email recipient before it starts sending email.

--Corby

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 04:07 AM . Last Modified: ‎2024-03-05 10:26 PM

0 Likes
0
1350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:07 AM . Last Modified: ‎2024-03-05 10:26 PM

I just finished a batch upgrade of AP9630/31s from 5.1.7 to 6.0.6.  After the upgrade I notice I wasn't receiving any email from the UPSs.  I guess the upgrade had reset the smtp server settings.  I didn't think this was too big of a problem because I have a script that can ftp my config.ini to all the UPSs.  However that did not fix the problem.  I figured out that I still have to open the smtp settings page, click apply(don't change any settings, just click apply), then test the email receipt and then everything is good.  I assume this is not normal.  Any workaround to this?  I really don't want to have to do this 159 times.  I also noticed in some cases that if I add a new user via mass ftp'ing the config.ini, I still have to test that email recipient before it starts sending email.

--Corby

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Anonymous user
Not applicable

Posted: ‎2021-07-01 04:07 AM . Last Modified: ‎2024-03-05 10:26 PM

0 Likes
0
1350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:07 AM . Last Modified: ‎2024-03-05 10:26 PM

I'm having similar issues as well. After I uploaded new .ini files to re-set the 'from' address for outgoing mail to 200-ish UPSes, it still wasn't working. I noticed that if I go in via telnet and type 'email', the route is "local", and it works if I change it to "custom". In the web-management system, the equivalent is configuration -> notification -> e-mail -> recipients, click recipient address, change "server" to "custom", at which point it un-greys the SMTP server information I entered on the e-mail notification server page (or via .ini upload).

I can't find any differences between ini files when the server/route is set to 'local' vs. 'custom'. I could write an expect script to fix all my UPSes, but as uploading a .ini file is already part of our install procedure, I'd like it to happen at that point for new UPSes rather than creating an additional step for our installers. Is that at all possible?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:07 AM . Last Modified: ‎2024-03-05 10:26 PM

0 Likes
0
1350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:07 AM . Last Modified: ‎2024-03-05 10:26 PM

I logged a bug personally on the mapping of local SMTP server when you ugprade from v5.1.X to v6.0.X because the local SMTP server was mapping to Custom SMTP instead of Local SMTP where then the settings for Server for the particular recipient were still on Local which was blank after the upgrade. That will be fixed in a future version. I too just changed my setting to Custom and it was fine but still required me to have to do that to get my notifications working.

I believe the value you'll want to see if its using Custom or not is EmailReceiver1UseCommon=disabled - if its set to Custom, you'll see it say disabled and when it is enabled, it will be set to use the route defined in EmailReceiver#Route value (local or recipients).

Now that we're talking about it, that might be one of those things I see if we can make more clear for the future.

I also missed this original post some how so Corby A, please let me know if you still need help with that.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:07 AM . Last Modified: ‎2024-03-05 10:26 PM

0 Likes
0
1350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:07 AM . Last Modified: ‎2024-03-05 10:26 PM

That helps, but it doesn't do me any good because mass configuration via ftp'ing .ini files doesn't change any of the configs.  If I set one card to use local or custom servers, download the config.ini, then upload it to another NMC2, the receiving card doesn't change its config.  I also suffer from the same as this http://forums.apc.com/message/48825#48825

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:07 AM . Last Modified: ‎2024-03-05 10:26 PM

0 Likes
0
1350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:07 AM . Last Modified: ‎2024-03-05 10:26 PM

Angela, I am seeing EmailReceiver1UseCommon=disabled in the downloaded config file, and that's also what I'm uploading, but it always says 'local' when I view the configuration via telnet/web. so if I'm understanding you correctly that that's supposed to change it to 'custom', I guess something might not be working right.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:07 AM . Last Modified: ‎2024-03-05 10:26 PM

0 Likes
0
1350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:07 AM . Last Modified: ‎2024-03-05 10:26 PM

Ok let me see here.

Ok, my mistake # 1 - I checked my card and my recipient was on local server, not custom when I checked this embarassedembarassedcry Sorry.

I'm changing it now, then redownloading my config.ini. Not all that much changed though.. hmm.

Anyway, here are the fields I see relating to a custom SMTP server for recipient 1.

EmailReceiver1Enable=enabled

EmailReceiver1Address=

EmailReceiver1Format=Long

EmailReceiver1UseCommon=disabled

EmailReceiver1FromName=UPS(at)mydomain.com

EmailReceiver1ServerName=

EmailReceiver1Port=25

EmailReceiver1Auth=enabled (i enabled it)

EmailReceiver1Username=testing (my authentication username)

EmailReceiver1SSLMode=none (i am using plain text authentication)

I think the key is going to be filling out UseCommon=disabled and then the custom server is still under EmailReciever#ServerName.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:07 AM . Last Modified: ‎2024-03-05 10:26 PM

0 Likes
0
1350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:07 AM . Last Modified: ‎2024-03-05 10:26 PM

OK, I think I figured it out. You talked about EmailReceiver#Route earlier, and I tried it, but I think I didn't have the 'C' in Custom capitalized, so when it didn't work, I just removed that line. I also didn't think I'd seen it in the downloaded config file, but I checked a couple other UPSes, and there it was, set to 'Local'. What you had in post 5 was basically what I was using, so putting it all together, it looks like it works.

EmailFromName=my_sender@example.com

EmailServerName=my_server.example.com

EmailServerPort=25

EmailServerAuth=disabled

EmailServerUsername=User

EmailServerSSLMode=none

EmailServerCertRequired=disabled

EmailServerCertFilename=""

EmailReceiver1Enable=enabled

EmailReceiver1Address=my_recipient@example.com

EmailReceiver1Format=Long

EmailReceiver1Language=enUs

EmailReceiver1UseCommon=disabled

EmailReceiver1Route=Custom

EmailReceiver1FromName=my_sender@example.com

EmailReceiver1ServerName=my_server.example.com

EmailReceiver1Port=25

EmailReceiver1Auth=disabled

EmailReceiver1Username=User

EmailReceiver1SSLMode=none

EmailReceiver1CertRequired=disabled

EmailReceiver1CertFilename=""

Thank you!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:07 AM . Last Modified: ‎2024-03-05 10:26 PM

0 Likes
0
1350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:07 AM . Last Modified: ‎2024-03-05 10:26 PM

No problem. But I am still confused because I had mine set to custom and nowhere in my config.ini did it say the word Custom. If it works, fine, but maybe there is something wrong here. I will look further into it on Monday.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 04:07 AM . Last Modified: ‎2024-03-05 10:26 PM

0 Likes
0
1351
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:07 AM . Last Modified: ‎2024-03-05 10:26 PM

I just finished a batch upgrade of AP9630/31s from 5.1.7 to 6.0.6.  After the upgrade I notice I wasn't receiving any email from the UPSs.  I guess the upgrade had reset the smtp server settings.  I didn't think this was too big of a problem because I have a script that can ftp my config.ini to all the UPSs.  However that did not fix the problem.  I figured out that I still have to open the smtp settings page, click apply(don't change any settings, just click apply), then test the email receipt and then everything is good.  I assume this is not normal.  Any workaround to this?  I really don't want to have to do this 159 times.  I also noticed in some cases that if I add a new user via mass ftp'ing the config.ini, I still have to test that email recipient before it starts sending email.

--Corby

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore