EASY UPS 3S 40 Kva failed
My EASY UPS 3S 40Kva stopped working and its shows this message :
01 REC SOFT START UNAVAILABLE.
Please any recommendations ?
Thanks a lot
- Tags:
- english
Authentication Failed.
- Authentication Ticket Mismatched, failed authentication.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-17 07:48 AM . Last Modified: 2023-04-17 08:27 AM
Hi Jack
I suggest you contact your local Schneider Electric support department
https://www.se.com/ie/en/work/support/customer-care/contact-schneider-electric.jsp
Please select and filter your country top left of webpage.
We would need the Serial and model number of the UPS but from what you describe I think there may be an issue with the input section for the UPS and a trained Field Service Engineer is required to replace either or any of the following:
40 kVA input power board
40 kVA rectifier power board x 3
Rectifier bus connection board
or Driver signal interface board
Hope this helps
Regards
John Coen