Discharged Battery Bug (Smart-UPS 3000 RM XL)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Discharged Battery Bug (Smart-UPS 3000 RM XL)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-07 10:13 PM . Last Modified: ‎2024-03-04 10:54 PM

0 Likes
6
4031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:13 PM . Last Modified: ‎2024-03-04 10:54 PM

Discharged Battery Bug (Smart-UPS 3000 RM XL)

Hello

We changed the BatteriePacks (3 Packs) becouse the Device said:

Discharged Battery
The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.

After the change we made 

  • UPS Self-Test
  • Runtime Calibration

But we still get Mails with this Problem. 

The Battery Capacity was 0% after we changed the packs and after 2 days it went to 100%. 

Load in Watts are at 65% (like bevore the change).

We made a Firmware upgrade (to the same Version because there was no new one)

Model Number: AP9617
Serial Number: JA0243038681
Hardware Revision: A10
Manufacture Date: 10/27/2002
MAC Address: 00 C0 B7 67 80 50
Management Uptime: 3 Days 1 Hour 11 Minutes
Application Module
   
Name: sumx
Version: v3.7.2
Date: 02/02/2010
Time: 19:08:16

APC | UPS Network Management Card

APC OS (AOS)
   
Name: aos
Version: v3.7.3
Date: 02/02/2010
Time: 17:05:14

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 3000
  • battery
  • bug
  • discharged
  • rm
  • smart-ups
  • xl
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:14 PM . Last Modified: ‎2024-03-04 10:53 PM

0 Likes
0
4030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:14 PM . Last Modified: ‎2024-03-04 10:53 PM

I can't provide it is why I asked if you came across the procedure online which many people do so I just figured I'd ask. If done improperly, it can damage the UPS and we stopped providing it as a solution for liability reasons so I was suggesting it if you didn't want to try the manual calibration originally. I can give you the constant "value" you need to set it to. This UPS's value is "89" and you can likely find instructions online on how to do it. If you get stuck, let me know but I just can't get in the habit of sending it to everyone individually but I'd also like you to have a functional UPS. 

Also, by using the config.ini, I noticed you disabled many of the UPS events from being logged in the UPS event log. I wasn't sure if that was intentional or not.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:13 PM . Last Modified: ‎2024-03-04 10:54 PM

0 Likes
0
4030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:13 PM . Last Modified: ‎2024-03-04 10:54 PM

Can you share the event.txt, and data.txt, and config.ini files from your management card? You can attach them here to the post. The model/firmware you're referencing is for an AP9617 network management card only. We need to know the SKU of the UPS, i.e. SUA1000I or similar. It'd be on the white sticker on the UPS itself.

We also need to know how much runtime the UPS is reporting and knowing that and seeing the logs can help us make a recommendation to you on how to proceed.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 10:13 PM . Last Modified: ‎2024-03-04 10:54 PM

0 Likes
0
4030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:13 PM . Last Modified: ‎2024-03-04 10:54 PM

I dont know how to export the config.ini...

We got the network management card "AP9617" in your device. 

This is the email we get 

Serial # : JA0243038681
Device Ser #: JS0833009502
Date: 04/05/2015
Time: 12:27:00
Code: 0x0107

Critical - UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.

In the UPS Section "Overview" it says:

APC | UPS Network Management Card

Runtime Remaining: 0 minutes

APC | UPS Network Management Card

Self-Test: Passed on April 05, 2015

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:13 PM . Last Modified: ‎2024-03-04 10:53 PM

0 Likes
0
4030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:13 PM . Last Modified: ‎2024-03-04 10:53 PM

Sorry, here are some instructions on exporting the full logs and configuration files -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156131 

What you provided doesn't show me what I need to see unfortunately beyond the fact runtime shows as 0 minutes.

Based on what you did share, it sounds like you may need to reset the "battery constant" that you may have saw mentioned online prior to posting here. We aren't supposed to really give out the procedure anymore since if done incorrectly, could render the UPS unusable. I requires a serial connection to the UPS to change a value. Have you seen this referenced anywhere yet? I could give you the value if you can run the procedure at your own risk. Normally we'd suggest a calibration first but it sounded like that didn't work.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:14 PM . Last Modified: ‎2024-03-04 10:53 PM

0 Likes
0
4030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:14 PM . Last Modified: ‎2024-03-04 10:53 PM

Hi Tobias,

No, I am talking about adjusting/setting battery constants. That is a manual calibration which may be an option to try as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 10:14 PM . Last Modified: ‎2024-03-04 10:53 PM

0 Likes
0
4030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:14 PM . Last Modified: ‎2024-03-04 10:53 PM

hi Angela 

Can you give me a "how to" for the solution " adjusting/setting battery constants" you are talking about? 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:14 PM . Last Modified: ‎2024-03-04 10:53 PM

0 Likes
0
4031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:14 PM . Last Modified: ‎2024-03-04 10:53 PM

I can't provide it is why I asked if you came across the procedure online which many people do so I just figured I'd ask. If done improperly, it can damage the UPS and we stopped providing it as a solution for liability reasons so I was suggesting it if you didn't want to try the manual calibration originally. I can give you the constant "value" you need to set it to. This UPS's value is "89" and you can likely find instructions online on how to do it. If you get stuck, let me know but I just can't get in the habit of sending it to everyone individually but I'd also like you to have a functional UPS. 

Also, by using the config.ini, I noticed you disabled many of the UPS events from being logged in the UPS event log. I wasn't sure if that was intentional or not.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore