We are using Smart-UPS 3000 RM with 9630 Management card. I got the following message. I tried to replace with a new battery and cold reboot the UPS , but still get the message of "the battery power is too low to support the load" and "Discharged Battery" Alarm
What can I do ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:49 AM . Last Modified: 2024-03-12 03:20 AM
Ok, it is likely that the UPS needs to be calibrated. See how your runtime reported is 3 minutes - and you have a very low load? This likely did not update properly after you replaced the batteries a month ago.
Essentially, you should attempt a runtime calibration which you can issue via the Network Management Card under UPS->Diagnostics. If this does not work properly, let me know. We'll need to attempt a few other steps and for those other steps, then I need to know the exact SKU of the UPS from the rear of it on the white sticker please.
Lastly, as more of a supplement, there is more explanation here (Why are the battery charge LEDs flashing on a Smart-UPS? | FAQs | Schneider Electric US). We may try the other steps outlined here but we may do one that is not mentioned there.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:49 AM . Last Modified: 2024-03-12 03:20 AM
My first thought is to check the following settings:
Then:
Let's start there. This may be just a setting configuration issue or if the batteries are lower, you may just have low runtime available now.
Alternatively, I can read this information from the event.txt, data.txt and config.ini files if you want to provide those. (Instructions here -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...)
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:49 AM . Last Modified: 2024-03-12 03:20 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:49 AM . Last Modified: 2024-03-12 03:20 AM
Hi Angela,
Thanks for your assistance.
Status of the UPS is as below:
Last Battery Transfer: | Due to software command or UPS's test control | ||
Internal Temperature: | 24.7°C | ||
Runtime Remaining: | 3min | ||
Power | |||
Input Voltage: | 117.3 VAC | ||
Output Voltage: | 117.3 VAC | ||
Frequency: | 60.0 Hz | ||
Load | |||
Load Power: | 9.1 %Watts | ||
Apparent Load Power: | 9.1 %VA | ||
Load Current: | 2.3 Amps | ||
Battery | |||
Capacity: | 100.0 % | ||
Battery Voltage: | 55.08 VDC | ||
External Batteries: | 0 |
Low Battery Duration: 2 mins (never be changed, by default)
How old are the batteries: New battery , Just changed it at last month.
The event.txt, data.txt, config.ini are compressed to a zip file at below link
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:49 AM . Last Modified: 2024-03-12 03:20 AM
Ok, it is likely that the UPS needs to be calibrated. See how your runtime reported is 3 minutes - and you have a very low load? This likely did not update properly after you replaced the batteries a month ago.
Essentially, you should attempt a runtime calibration which you can issue via the Network Management Card under UPS->Diagnostics. If this does not work properly, let me know. We'll need to attempt a few other steps and for those other steps, then I need to know the exact SKU of the UPS from the rear of it on the white sticker please.
Lastly, as more of a supplement, there is more explanation here (Why are the battery charge LEDs flashing on a Smart-UPS? | FAQs | Schneider Electric US). We may try the other steps outlined here but we may do one that is not mentioned there.