Discharge Battery Alarm , what should I do ?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Discharge Battery Alarm , what should I do ?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:49 AM . Last Modified: ‎2024-03-12 03:20 AM

0 Likes
3
2321
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:49 AM . Last Modified: ‎2024-03-12 03:20 AM

Discharge Battery Alarm , what should I do ?

We are using Smart-UPS 3000 RM with 9630 Management card.    I got the following message.  I tried to replace with a new battery and cold reboot the UPS , but still get the message of  "the battery power is too low to support the load" and  "Discharged Battery" Alarm


What can I do ?



2245_ups alarm.jpg

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:49 AM . Last Modified: ‎2024-03-12 03:20 AM

0 Likes
0
2320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:49 AM . Last Modified: ‎2024-03-12 03:20 AM

Ok, it is likely that the UPS needs to be calibrated. See how your runtime reported is 3 minutes - and you have a very low load? This likely did not update properly after you replaced the batteries a month ago.

Essentially, you should attempt a runtime calibration which you can issue via the Network Management Card under UPS->Diagnostics. If this does not work properly, let me know. We'll need to attempt a few other steps and for those other steps, then I need to know the exact SKU of the UPS from the rear of it on the white sticker please.

Lastly, as more of a supplement, there is more explanation here (Why are the battery charge LEDs flashing on a Smart-UPS? | FAQs | Schneider Electric US). We may try the other steps outlined here but we may do one that is not mentioned there.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:49 AM . Last Modified: ‎2024-03-12 03:20 AM

0 Likes
0
2320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:49 AM . Last Modified: ‎2024-03-12 03:20 AM

My first thought is to check the following settings:

  • Verify the UPS runtime under the UPS->status or overview menu (is the value normal?)
  • Check under UPS->Shutdown and let me know what the low battery duration value is set to. (did you recently change this)

Then:

  • How old are the batteries?

Let's start there. This may be just a setting configuration issue or if the batteries are lower, you may just have low runtime available now.

Alternatively, I can read this information from the event.txt, data.txt and config.ini files if you want to provide those. (Instructions here -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...)

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:49 AM . Last Modified: ‎2024-03-12 03:20 AM

0 Likes
0
2320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:49 AM . Last Modified: ‎2024-03-12 03:20 AM

Hi Angela,


Thanks for your assistance.  



Status of the UPS is as below:


Last Battery Transfer:Due to software command or UPS's test control
Internal Temperature:24.7°C
Runtime Remaining:3min
Power
Input Voltage:117.3 VAC
Output Voltage:117.3 VAC
Frequency:60.0 Hz
Load
Load Power:9.1 %Watts
Apparent Load Power:9.1 %VA
Load Current:2.3 Amps
Battery
Capacity:100.0 %
Battery Voltage:55.08 VDC
External Batteries:0


Low Battery Duration:        2 mins (never be changed, by default)

How old are the batteries:  New battery , Just changed it at last month.


The event.txt, data.txt, config.ini are compressed to a zip file at below link

http://speedy.sh/7BDbt/10.10.74.182.zip

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:49 AM . Last Modified: ‎2024-03-12 03:20 AM

0 Likes
0
2321
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:49 AM . Last Modified: ‎2024-03-12 03:20 AM

Ok, it is likely that the UPS needs to be calibrated. See how your runtime reported is 3 minutes - and you have a very low load? This likely did not update properly after you replaced the batteries a month ago.

Essentially, you should attempt a runtime calibration which you can issue via the Network Management Card under UPS->Diagnostics. If this does not work properly, let me know. We'll need to attempt a few other steps and for those other steps, then I need to know the exact SKU of the UPS from the rear of it on the white sticker please.

Lastly, as more of a supplement, there is more explanation here (Why are the battery charge LEDs flashing on a Smart-UPS? | FAQs | Schneider Electric US). We may try the other steps outlined here but we may do one that is not mentioned there.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of