I've searched the knowledge base but cannot find what I'm looking for.
When looking at the data log I would like to know what each of the columns stand for:
Vmin | Vmax | Vout | Iout | %Wout | %out | FrqOut | %Cap | Vbat | Tups |
Not having any luck so far. I do know that Vmin is the minimum voltage the UPS received and Vmax is the max, but Vout, Iout, %Wout, %out, FrqOut, %cap, Vbat, Tups I really have no clue.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:14 AM . Last Modified: 2024-03-05 02:27 AM
This saved me asking the question 🙂
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:14 AM . Last Modified: 2024-03-05 02:27 AM
What you see depends on the UPS. Here is what I can tell you.
Vmin = Minimum voltage seen across the logging interval
Vmax = Maximum voltage seen across the logging interval
Vout = Voltage on the output of the UPS
Iout = Current Out (I represents current in the equation V=IR)
%Wout = Percentage of Wattage based on total UPS capacity that you have on your UPS
%Out = This doesn't say anything else like %VA out? If so, it'd be percentage of Volt Amps out based on UPS capacity. *edit* I also found a UPS of mine that says this and I believe it would be the %VA out for sure even though it does not say it since that is what is available in the web UI else where.
FrqOut = Frequency Output of the UPS
%Cap = Percentage Battery Capacity
Vbat = Battery Voltage
Tups = Internal Temperature of the UPS in either F or C
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:14 AM . Last Modified: 2024-03-05 02:27 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:14 AM . Last Modified: 2024-03-05 02:27 AM
Thank you!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:14 AM . Last Modified: 2024-03-05 02:27 AM
This saved me asking the question 🙂
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.