Current draw of RM3000SM2U (208 volts) during recharge?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Current draw of RM3000SM2U (208 volts) during recharge?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-25 10:49 PM . Last Modified: β€Ž2024-03-19 03:27 AM

0 Likes
4
1056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-25 10:49 PM . Last Modified: β€Ž2024-03-19 03:27 AM

Current draw of RM3000SM2U (208 volts) during recharge?

I need to move a data rack which has an RM3000SM2u, 208 volt UPS to a generator-backed circuit.

I'm trying to help the building manager guarantee that we're not going to exceed the generator's output load.

The generator takes about 10 seconds to start from a lights out event.

The UPS is currently running at about 38% of capacity, which uses 5.3 amps at 208 volts.

What kind of load can we expect the UPS to create when power is restored? I realize the current draw is probably going to be above our usual 5.3 amps, as some of the current draw of the device is going to be recharging the battery. I would hope that the device doesn't take on the full 20 amps available in the circuit it is plugged into πŸ˜‰

Labels
  • Labels:
  • Server Room & Data Center Design Best Practices
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-25 10:50 PM . Last Modified: β€Ž2024-03-19 03:27 AM

0 Likes
0
1056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-25 10:50 PM . Last Modified: β€Ž2024-03-19 03:27 AM

alrighty. i asked around and did not have an exact figure but was told ~92%. the charger is still max 175 watts but it can vary based on certain conditions (battery temperature, etc). i think the most accurate number for total consumption of the unit while charging the batteries is close to 275 watts.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-25 10:49 PM . Last Modified: β€Ž2024-03-19 03:27 AM

0 Likes
0
1056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-25 10:49 PM . Last Modified: β€Ž2024-03-19 03:27 AM

Watts Are Watts

12 Watts At 1.5 Volts Is The Same As 12 Watts At 1000,000 Volts

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-25 10:50 PM . Last Modified: β€Ž2024-03-19 03:27 AM

0 Likes
0
1056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-25 10:50 PM . Last Modified: β€Ž2024-03-19 03:27 AM

if this is an [SUA3000RM2U|www.apc.com/resource/include/techspec_index.cfm?base_sku=SUA3000RM2U] as I'd suspect, then it uses 175W to charge.

here are a few notes you need to consider for the power consumption during charging.

Internal Power Consumption is the amount of power coming into the UPS that does not leave to support the load, and is due to internal conversion to either heat or stored battery charge. Internal power consumption is equal to the inefficiency times the Watt rating at full load

Example: SURT5000XLI (full load) is rated at 3500 watts and 92% efficiency.The internal consumption is equal to 3500 watts * (100%-92%)=280 watts

As far as calculating the extra power consumption when the batteries are fully charging, you would add the charger watt rating to the internal power consumption. However, calling this internal power consumption may not be theoretically correct since the energy is being stored for later use, not dissipated and lost. There is a percentage of the charger energy that is also lost due to inefficiencies and secondary electro-chemical processes, but getting into this detail is not practical.

Battery charger for SURT5000XLI: 341 W

Total current drawn without load and with fully discharged batteries:
(280W+341W) / 230V (Mains Voltage) = 2.7A

efficiency is on the apc.com link i showed and i gave you the charger rating now πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-25 10:50 PM . Last Modified: β€Ž2024-03-19 03:27 AM

0 Likes
0
1056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-25 10:50 PM . Last Modified: β€Ž2024-03-19 03:27 AM

Close...it's the 208 volt model (not the 120 volt model) πŸ˜‰

208 is a common voltage in American office buildings (well, for supplying large amounts of power to server rooms and HVAC, you usually don't go strolling down the hallway and into cubicles and see 208 volt outlets). It is apparently a very easy voltage to produce from a 480 volt three phase transformer.

http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SUA3000RMT2U&total_watts=50...

Can't find anything on the effeciency specs, though, for the 208 model... 😞

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-25 10:50 PM . Last Modified: β€Ž2024-03-19 03:27 AM

0 Likes
0
1057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-25 10:50 PM . Last Modified: β€Ž2024-03-19 03:27 AM

alrighty. i asked around and did not have an exact figure but was told ~92%. the charger is still max 175 watts but it can vary based on certain conditions (battery temperature, etc). i think the most accurate number for total consumption of the unit while charging the batteries is close to 275 watts.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore