Posted: 2021-07-0904:20 AM. Last Modified: 2024-02-1411:03 PM
Hello. The ACSC100 is usually connected to the utility power not a UPS. This is due to the high inrush current the unit pulls when the compressor is starting up. This can trip the breakers on a UPS or overload the UPS. It is recommended that the unit is connect to utility power for these reasons.