Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Connection to serial port via USB-serial adapter

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Connection to serial port via USB-serial adapter
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
5059
voidstar_apc
voidstar_apc
196
Teken
Teken
164
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:30 PM

0 Likes
12
71489
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:30 PM

Connection to serial port via USB-serial adapter

Hi,
I regularly use a laptop to configure several APC smart-UPS via command line and putty. Up until a week ago the laptop was windows 7 starter edition. I have since wiped this and put Windows 7 Enterprise and reinstalled all the drivers and necessary software. However since this reinstall I am unable to connect to any APC UPS.

I've tried various drivers for the USB-serial adapter. It is a Belkin F5U103V. The odd thing is that I can connect to Cisco switches using the same adapter so there isn't a problem with the driver as far as I can tell.

The serial settings I am using are 38400, 8, 0, 1, XON XOFF.

I'm just getting no response in the putty window after initialising connection. Have tried pressing enter several times to jog it along.

I realise that this isn't an APC issue as such, but I wondered whether anyone else had found a solution to this. Failing that I'm going to have to reinstall windows 7 starter edition and try again with that.

Cheers in advance.

Message was edited by: The Goatreich

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

0 Likes
0
71444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

All sorted!!! Reseated the NIC and it all came to life.

Cheers for your help all.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

0 Likes
0
71445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

Hi..
If you wish to communicate with APC smart UPS thru serial, the settings on your hyperternimal are:-
Baud rate = 2400 , Stop bit = 1, Data bit = 8, Flow control = None and parity = None.
If the UPS 's port is RJ45 type, baud rate = 9600.

Thanks and regards

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

0 Likes
0
71445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

Hi,
I regularly use a laptop to configure several APC smart-UPS via command line and putty. Up until a week ago the laptop was windows 7 starter edition. I have since wiped this and put Windows 7 Enterprise and reinstalled all the drivers and necessary software. However since this reinstall I am unable to connect to any APC UPS.

I've tried various drivers for the USB-serial adapter. It is a Belkin F5U103V. The odd thing is that I can connect to Cisco switches using the same adapter so there isn't a problem with the driver as far as I can tell.

The serial settings I am using are 38400, 8, 0, 1, XON XOFF.

I'm just getting no response in the putty window after initialising connection. Have tried pressing enter several times to jog it along.

I realise that this isn't an APC issue as such, but I wondered whether anyone else had found a solution to this. Failing that I'm going to have to reinstall windows 7 starter edition and try again with that.

Cheers in advance.

Message was edited by: The Goatreich

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

0 Likes
0
71444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

what UPS are you trying to connect to? only APC netbotz devices connect at 38400. most UPSs use either 9600 or 2400 baud rate, depending on the model and use None for flow control.

if you tell me the exact model of the UPS, i can give you the definite port speed/settings.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

0 Likes
0
71444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

It's a SmartUPS 3000 (black 2U model). I've tried dropping the baud rate down to 9600 as a test. Admittedly I didn't change the flow control though.

Message was edited by: The Goatreich

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

0 Likes
0
71444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

Hi,
yes it has a AP9617 NIC in the smart slot. That is why I'm trying to connect in the first place as I need to reconfigure it.

I'm using a 940-1524D serial cable, and have now tried baud rate 2400, data bits 8, Stop bits 1, Parity None, Flow Control None.

I just get a blank terminal window.

I've also tried a different cable with the same results.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

0 Likes
0
71445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

All sorted!!! Reseated the NIC and it all came to life.

Cheers for your help all.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

0 Likes
0
71445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

Having the incorrect baud rate and flow control had stopped me connecting to the other UPSs.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

0 Likes
0
71444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

hi,

 

I have an SRT 10kva ups with a sys error 02000. i have a cable with rj45 type and it doesnt respond. there is also a usb port behind the ups, what are the settings for the usb port connection

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

0 Likes
0
71445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

On 11/21/2019 8:43 AM, Katongo said:

hi,

 

I have an SRT 10kva ups with a sys error 02000. i have a cable with rj45 type and it doesnt respond. there is also a usb port behind the ups, what are the settings for the usb port connection

Hi Katongo,

If you want to access the console view of the embedded network interface, you can only use the TRS to DB9 cable (PN: 940-0299). Looks like the picture below. There is a TRS console port beside the Ethernet port that you can connect to.

SDYz3fSUHZTUTfbJsciU8g%3D%3D.pngSDYz3fSUHZTUTfbJsciU8g%3D%3D.png

0HOnhnDZLYEkphDeVX2ABQ%3D%3D.png0HOnhnDZLYEkphDeVX2ABQ%3D%3D.png

Setting are 9600, 8, 1, None, None on a terminal program. Default username and password is "apc".

The USB and Serial port on the UPS is applicable only if you will use PowerChute Business Edition. 

As for the error, I recommend for you to contact local support.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

0 Likes
0
71445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

Hi,

There is no need to connect the cable. The 0200 error indicates an Oscillator event. To correct you should brain dead the UPS. See Schneider Electric FAQ FA156611 for assistance with "How to perform a cold start and brain dead of Smart-UPS" 

If the issue returns after the brain dead procedure they UPS should be replaced. 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

engineeringCASAUPS
engineeringCASAUPS
Explorer

Posted: ‎2024-05-15 11:56 AM

0 Likes
0
45956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-15 11:56 AM

Hi, have a nice day, excuse me, I have the same problem, I want to configure a SURTD6000RMXLP3U but the cable is damaged and I don't know which pins are used and which baud rate is necessary. Please, Do you have the diagram of conection for this cable. (The serial com is rj45 and I have the cable serial to USB working). Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

collinskawanga
collinskawanga Explorer
Explorer

Posted: ‎2025-08-20 06:26 PM

0 Likes
0
15195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-20 06:26 PM

I have a SRTG5KXLI which has a display not working. the unit itself is fine. apparently it was switched off during maintenance using the power button but it cant be switched back on for the main output. only the controlled outs are working. How ca one connect and switch on the main output? Please advise

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore