Confused about properly setting up PCNS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Confused about properly setting up PCNS
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:54 AM . Last Modified: ‎2024-03-11 12:20 AM

0 Likes
5
669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:54 AM . Last Modified: ‎2024-03-11 12:20 AM

Confused about properly setting up PCNS

Hi all, getting mixed responses from fellow colleges and forums I have been reading. What I have is 3 Smart-UPS SRT 8000's with 29 physical servers some of which are ESX hosts and 2 SAN devices. I have PCNS 4.2 for VMWare installed and have all hosts discovered, and PCNS installed on the physical servers. In order to shut these down gracefully what is the best way? Currently we are sitting at 1hr run time and would like to start shutting down when batteries are about 30 minutes remaining to ensure they turn of in time. Issue I have is how does the VM host shut down the VMS? We have about 117 VM's running, does the PCNS client need to be on each or the VMhost sends commands to turn off when the software tells it to?

A lot to ask, but being asked to install this 15 years after business started is making this challenging. 

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:55 AM . Last Modified: ‎2024-03-11 12:20 AM

0 Likes
0
669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:55 AM . Last Modified: ‎2024-03-11 12:20 AM

Hi,

On 9/17/2018 7:46 PM, Tom said:

Can PCNS be installed on SAN devices (Nimble)? 

No. Here is a link to the compatibility chart. http://www.apc.com/whitepaper/?um=200

On 9/17/2018 7:46 PM, Tom said:

Second question is about DRS on our VM Ware and PCNS. Within the software it has you choose then select timings for migrations. We're confused because we have it set to full automation within Vsphere, why do we also have to tell PCNS to do the same thing? We've read the instruction pages 31 on and its not making sense - probably over thinking it. 

You need to set the migration delay so that PCNS will wait the delay before attempting to power down the VMs. If you do not while DRS is moving the VMs PCNS will be powering them down.

On 9/17/2018 7:46 PM, Tom said:

Final question, there a way to test configs, shutdown sequences etc. without actually pulling the power?

You can trigger the process via the NMC. Open the NMC interface and go to Control - UPS. Depending on the UPS model you can tell the UPS to reboot,  turn off UPS, reboot outlet groups, or turn off outlet groups. Then select signal PowerChute clients and the NMC will inform PCNS that it needs to start the power down process. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:54 AM . Last Modified: ‎2024-03-11 12:20 AM

0 Likes
0
669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:54 AM . Last Modified: ‎2024-03-11 12:20 AM

Hi,

On 8/28/2018 7:03 PM, Tom said:

I have PCNS 4.2 for VMWare installed and have all hosts discovered, and PCNS installed on the physical servers.

Question, do you have PCNS on the Windows server configured for communications with vCenter Server and do you have PCNS configured for 3 redundant UPS?

For information on PCNS and redundant UPS see page 4 of the User's Guide and Application Note 98   

I will make the assumption that the above is true. PCNS is configured for redundant UPS and with vCenter Server. With that being the case, the simples solution is to set the low battery threshold on each NMC to 30 minutes. When the UPS falls below 30 minutes of runtime the NMC informs PCNS. When PCNS see that 2 of the 3 UPS have fallen below 30 minutes of runtime a critical alarm is triggered and the shut down process will start.

You should configure PCNS to shut the VMs down and set the delay to accommodate the time needed to shut all of the VMs down. In the image below I have the VM shutdown delay set for 2 minutes and VM start up delay of 2 minutes.

k9bTFUPeWXxjlHhs3v0n%2FA%3D%3D.pngk9bTFUPeWXxjlHhs3v0n%2FA%3D%3D.png

PowerChute will wait for the VM shutdown delay to elapse and then begin to power down the hosts. The host will be powered down base on the order they appear in the host protection list. See page 10 of the User's Guide for more information. 

For more information on on PCNS and VMware see Application Note 180 and the User's Guide. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:54 AM . Last Modified: ‎2024-03-11 12:20 AM

0 Likes
0
669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:54 AM . Last Modified: ‎2024-03-11 12:20 AM

A few more questions for clarification as this seems to be a large undertaking. If AC power was restored, does PCNS shutdown sequences stop the process or does it have to finish powering everything down. Also is creating your own shutdown command file best practice or should we rely on PCNS to send the commands. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:54 AM . Last Modified: ‎2024-03-11 12:20 AM

0 Likes
0
669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:54 AM . Last Modified: ‎2024-03-11 12:20 AM

Hi,

On 9/4/2018 12:07 PM, Tom said:

A few more questions for clarification as this seems to be a large undertaking. If AC power was restored, does PCNS shutdown sequences stop the process or does it have to finish powering everything down.

Once PowerChute has started the shutdown process it must be complete. Once the system/s are down they can then be powered back up. 

On 9/4/2018 12:07 PM, Tom said:

Also is creating your own shutdown command file best practice or should we rely on PCNS to send the commands. 

I recommend using the once provided with the software. They have been tested in our labs and by many, many other users. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:55 AM . Last Modified: ‎2024-03-11 12:20 AM

0 Likes
0
669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:55 AM . Last Modified: ‎2024-03-11 12:20 AM

Thanks Bill! Final 3 questions (hopefully)

Can PCNS be installed on SAN devices (Nimble)? 

Second question is about DRS on our VM Ware and PCNS. Within the software it has you choose then select timings for migrations. We're confused because we have it set to full automation within Vsphere, why do we also have to tell PCNS to do the same thing? We've read the instruction pages 31 on and its not making sense - probably over thinking it. 

Final question, there a way to test configs, shutdown sequences etc. without actually pulling the power? 

Thanks again!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:55 AM . Last Modified: ‎2024-03-11 12:20 AM

0 Likes
0
670
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:55 AM . Last Modified: ‎2024-03-11 12:20 AM

Hi,

On 9/17/2018 7:46 PM, Tom said:

Can PCNS be installed on SAN devices (Nimble)? 

No. Here is a link to the compatibility chart. http://www.apc.com/whitepaper/?um=200

On 9/17/2018 7:46 PM, Tom said:

Second question is about DRS on our VM Ware and PCNS. Within the software it has you choose then select timings for migrations. We're confused because we have it set to full automation within Vsphere, why do we also have to tell PCNS to do the same thing? We've read the instruction pages 31 on and its not making sense - probably over thinking it. 

You need to set the migration delay so that PCNS will wait the delay before attempting to power down the VMs. If you do not while DRS is moving the VMs PCNS will be powering them down.

On 9/17/2018 7:46 PM, Tom said:

Final question, there a way to test configs, shutdown sequences etc. without actually pulling the power?

You can trigger the process via the NMC. Open the NMC interface and go to Control - UPS. Depending on the UPS model you can tell the UPS to reboot,  turn off UPS, reboot outlet groups, or turn off outlet groups. Then select signal PowerChute clients and the NMC will inform PCNS that it needs to start the power down process. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of