Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Configuring Shutdown Delay with PowerChute

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Configuring Shutdown Delay with PowerChute
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 01:49 AM . Last Modified: ‎2024-02-29 10:31 PM

0 Likes
6
1526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:49 AM . Last Modified: ‎2024-02-29 10:31 PM

Configuring Shutdown Delay with PowerChute

Hello,

I am new to PowerChute and UPS units in a VMWare environemnt, so forgive my lack of knowledge.

I have PowerChute set up on a VM and it is connected to the IP address of the APC that is running the hosts and SAN for our VM environment.

I think things are going well, but I have 2 questions:

1. Where do I go to configure SMTP settings so that alerts that I have set up will notify me by email?

2. If it is not set by default, how do I delay the shutdown process of VMs when power is lost? I am thinking that if the power goes out for 10 minutes, our UPS should be able to carry the load for that period of time, and I don't want the VMs to start shutting down right away. Is this the default or do VMs start shutting down as soon as power is lost? Where do I find or see these settings?

I have logged into the PowerChute web interface as well as the APC interface and I don't see it anywhere.

Thanks!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:49 AM . Last Modified: ‎2024-02-29 10:31 PM

0 Likes
0
1526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:49 AM . Last Modified: ‎2024-02-29 10:31 PM

Hi,

On 10/21/2015 10:07 AM, Tyler said:

1. Where do I go to configure SMTP settings so that alerts that I have set up will notify me by email?

E-mail is configured on the UPS Network Management Card not in PowerChute. Help with configuring the Network Card can be found in the User's Guide. http://www.apc.com/prod_docs/results.cfm?DocType=User%20Manual&Query_Type=3&Value=98

On 10/21/2015 10:07 AM, Tyler said:

2. If it is not set by default, how do I delay the shutdown process of VMs when power is lost? I am thinking that if the power goes out for 10 minutes, our UPS should be able to carry the load for that period of time, and I don't want the VMs to start shutting down right away. Is this the default or do VMs start shutting down as soon as power is lost? Where do I find or see these settings?

PowerChute will automatically start a shutdown when the UPS reaches low battery. The low battery setting is found on the Network Management Care (see User's Guide link above). If you would like the shutdown to start after the UPS has been on battery for x minutes in the PCNS web interface go to Configure Events - UPS on Battery and select Shutdown, Then click on Enable Shutdown and enter a delay. 

Assuming your configuration is a single ESXi host and not part of a cluster the shutdown settings for the VMs are configured on the ESXi host. See Kbase FA159688 for assistance. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:49 AM . Last Modified: ‎2024-02-29 10:31 PM

0 Likes
0
1527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:49 AM . Last Modified: ‎2024-02-29 10:31 PM

Hi,

On 10/21/2015 10:07 AM, Tyler said:

1. Where do I go to configure SMTP settings so that alerts that I have set up will notify me by email?

E-mail is configured on the UPS Network Management Card not in PowerChute. Help with configuring the Network Card can be found in the User's Guide. http://www.apc.com/prod_docs/results.cfm?DocType=User%20Manual&Query_Type=3&Value=98

On 10/21/2015 10:07 AM, Tyler said:

2. If it is not set by default, how do I delay the shutdown process of VMs when power is lost? I am thinking that if the power goes out for 10 minutes, our UPS should be able to carry the load for that period of time, and I don't want the VMs to start shutting down right away. Is this the default or do VMs start shutting down as soon as power is lost? Where do I find or see these settings?

PowerChute will automatically start a shutdown when the UPS reaches low battery. The low battery setting is found on the Network Management Care (see User's Guide link above). If you would like the shutdown to start after the UPS has been on battery for x minutes in the PCNS web interface go to Configure Events - UPS on Battery and select Shutdown, Then click on Enable Shutdown and enter a delay. 

Assuming your configuration is a single ESXi host and not part of a cluster the shutdown settings for the VMs are configured on the ESXi host. See Kbase FA159688 for assistance. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:49 AM . Last Modified: ‎2024-02-29 10:31 PM

0 Likes
0
1525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:49 AM . Last Modified: ‎2024-02-29 10:31 PM

Thank you for that information. I was able to find and test the SMTP settings so thank you for that.

My VM environment is a dual host environment with HA turned on. Can you be more specific on where the low battery settings are found? I actually prefer that option over a timed shutdown, so thank you for explaining the default settings. By default, what is the low battery setting set to?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:50 AM . Last Modified: ‎2024-02-29 10:31 PM

0 Likes
0
1525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:50 AM . Last Modified: ‎2024-02-29 10:31 PM

Hi,

The default low battery setting is 2 minutes. The setting is on the NMC and is found under Configure - Shutdown for  NMC firmware version 6.x or under UPS - Shutdown for NMC firmware version 5.x. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:50 AM . Last Modified: ‎2024-02-29 10:31 PM

0 Likes
0
1526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:50 AM . Last Modified: ‎2024-02-29 10:31 PM

Bill,

So this means that when there is 2 min of power left on battery, the UPS will start sending shut down commands to PowerChute to start shutting down VMs? Am I understanding that correctly?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:50 AM . Last Modified: ‎2024-02-29 10:31 PM

0 Likes
0
1526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:50 AM . Last Modified: ‎2024-02-29 10:31 PM

Yes, that is correct. The default setting is 2 minutes. You should increase the delay to match the needed time it takes for the VMs and host to power down correctly plus an additional 2 minutes for safety. Example: VMs take 2 minutes to power down, the host take 2 minutes to power down so low battery should be set to 6 minutes.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:50 AM . Last Modified: ‎2024-02-29 10:31 PM

0 Likes
0
1526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:50 AM . Last Modified: ‎2024-02-29 10:31 PM

Thank you for all your help! I appreciate it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of