Posted: 2021-06-30 05:55 AM . Last Modified: 2024-03-08 01:51 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:55 AM . Last Modified: 2024-03-08 01:51 AM
SUA1500 UPS with w2k PC, USB connection.
PowerChute Business Edition Agent/Server/Console Installed.
In the console, under "Diagnostics>>Self-Test" I can see a button to run
a self-test (which I did), and it says,
Based on current UPS settings, a self-test will be run every two weeks.
However, there's no immediately obvious way to change the interval.
I remember I could set this interval with my previous UPS, an SU700NET,
so I'm a bit surprised that the functionality has been lost. Do I need some
special card (which I don't want to buy) to adjust this parameter?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:55 AM . Last Modified: 2024-03-08 01:51 AM
Todd,
Log into the PCBE Agent's web interface:
http://
Then go into Diagnostics. You can change the option from every 14 days to every 7, never, or on startup.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:55 AM . Last Modified: 2024-03-08 01:51 AM
Todd,
Log into the PCBE Agent's web interface:
http://
Then go into Diagnostics. You can change the option from every 14 days to every 7, never, or on startup.