Configuring APC Master Switch Power Controller

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Configuring APC Master Switch Power Controller
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 06:38 AM . Last Modified: β€Ž2024-03-18 01:14 AM

0 Likes
8
3199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 06:38 AM . Last Modified: β€Ž2024-03-18 01:14 AM

Configuring APC Master Switch Power Controller

Hello,

This is my first post on the forums.

What I have here is an old APC Master Switch Power Controller that has 8 NEMA 5-15 outlets, a 10Base-T Ethernet port, and a 9-pin male serial interface. It looks exactly like this one http://www.andovercg.com/datasheets/apc-ap9210-masterswitch.pdf same specs and everything. I am not sure what the model number is because it isn't printed or labeled on the unit anywhere, but I'm assuming it's a 9210 or something close.

My problem is I have no idea what the IP address of the unit is, and I don't have the serial cable for it, so I really have no means of communicating with the device. I work in a SOHO environment so I do not have much access to networking equipment to configure this thing - basically all I have is a laptop and a few straight-thru Ethernet cables. So what are my options for connecting to and configuring this thing? Would my best bet be to buy a generic 9-pin serial cable and configure the unit via terminal emulator?

Thanks,
-Austin

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • ap9210
  • console
  • master
  • masterswitch
  • power_controller
  • powerswitch
  • serial_cable
  • switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 06:38 AM . Last Modified: β€Ž2024-03-18 01:13 AM

0 Likes
0
3199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 06:38 AM . Last Modified: β€Ž2024-03-18 01:13 AM

I believe the model number is on the serial number label, which is a small rectangular white label with barcodes. If you have the rackmount ears attached, I think the label is under one of them. I might be thinking of the MAC address label, though, in which case the model / serial label would be on the bottom of the unit.

An AP9210 has the network cable connector directly on the beige chassis. An AP9211 (slightly newer) has the network cable plugged into an AP9606 management card (black faceplate) which is then mounted in the chassis. The newer models have the console and network ports on the outlet side of the unit.

[This thread|Referenced content removed] has some info on the default passwords, as well as an important security warning which you should read.

The preferred way to recover from a lost password on these was to contact APC support with the model and serial number, and they'd give you a special password valid only for that particular unit. I don't know if that service is still offered, since those units were obsoleted many years ago. The security warning I mentioned above is about a password that works on ALL units.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 06:38 AM . Last Modified: β€Ž2024-03-18 01:14 AM

0 Likes
0
3199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 06:38 AM . Last Modified: β€Ž2024-03-18 01:14 AM

Update:

Per your advice I was able to find the model number (AP9210), serial number, and MAC address of the unit by removing the rackmount ears on the sides - thanks!

Regarding connecting to the unit I ended up acquiring a generic DB9 null modem serial cable, connected one end to the serial port of my PC and the other to the console port on the powerswitch, set my hyper terminal settings (2400, 8 bits, no parity, 1 stop bit, and no flow control), but was not able to establish a session with the unit. After hitting enter several times and waiting several minutes I was left with just a blinking cursor. Any ideas as to what's going on here? Does this unit use a proprietary null modem cable by chance?

Thanks
-Austin

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 06:38 AM . Last Modified: β€Ž2024-03-18 01:14 AM

0 Likes
0
3199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 06:38 AM . Last Modified: β€Ž2024-03-18 01:14 AM

I forget if those old units run at 2400 or some other speed (9600 or 19200 are the likely alternatives). I also don't remember if these use the same 940-0024 proprietary cable as other APC units. Probably, as the AP9211 is the same box but with a removable SmartSlot management card. APC won't tell you the pinout and may say something about warranties, but your unit is long obsolete, so a web search for "apc 940-0024 pinout" would be useful.

Please be aware of the giant security hole I mentioned in my prior post - anyone who has access to the unit via either the serial or network ports can take complete control of it, lock you out, and turn off the outlets.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 06:38 AM . Last Modified: β€Ž2024-03-18 01:14 AM

0 Likes
0
3199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 06:38 AM . Last Modified: β€Ž2024-03-18 01:14 AM

Wow that was a fast reply! πŸ˜‰

I was looking at the wrong user guide and thus was entering the wrong bit rate settings in hyper terminal. After entering the correct bit rate (192000) I was able to establish a console connection with the unit. However, the password and default username have been changed, so I cannot gain access into the system settings. Any backdoors that I could use to gain access?

Much appreciated!
-Austin

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 06:38 AM . Last Modified: β€Ž2024-03-18 01:13 AM

0 Likes
0
3199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 06:38 AM . Last Modified: β€Ž2024-03-18 01:13 AM

As I'm a guest here on APC's forum, I'd like to remain on good terms with them. I strongly suggest you read the thread that I linked to in my first reply to you here, particularly my post in that other thread.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 06:38 AM . Last Modified: β€Ž2024-03-18 01:13 AM

0 Likes
0
3199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 06:38 AM . Last Modified: β€Ž2024-03-18 01:13 AM

Thanks Terry!

I have read and fully understand that this unit has a major security flaw. If this device were to be introduced onto our network it would be deployed behind a firewall, and would only be made accessible to specific users on the LAN.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: β€Ž2021-06-28 06:38 AM . Last Modified: β€Ž2024-03-18 01:13 AM

0 Likes
0
3199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 06:38 AM . Last Modified: β€Ž2024-03-18 01:13 AM

>
I have read and fully understand that this unit has a major security flaw.
>

I think Terry is saying that, in your case, it's also a feature.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 06:38 AM . Last Modified: β€Ž2024-03-18 01:13 AM

0 Likes
0
3199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 06:38 AM . Last Modified: β€Ž2024-03-18 01:13 AM

πŸ˜‰

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 06:38 AM . Last Modified: β€Ž2024-03-18 01:13 AM

0 Likes
0
3200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 06:38 AM . Last Modified: β€Ž2024-03-18 01:13 AM

I believe the model number is on the serial number label, which is a small rectangular white label with barcodes. If you have the rackmount ears attached, I think the label is under one of them. I might be thinking of the MAC address label, though, in which case the model / serial label would be on the bottom of the unit.

An AP9210 has the network cable connector directly on the beige chassis. An AP9211 (slightly newer) has the network cable plugged into an AP9606 management card (black faceplate) which is then mounted in the chassis. The newer models have the console and network ports on the outlet side of the unit.

[This thread|Referenced content removed] has some info on the default passwords, as well as an important security warning which you should read.

The preferred way to recover from a lost password on these was to contact APC support with the model and serial number, and they'd give you a special password valid only for that particular unit. I don't know if that service is still offered, since those units were obsoleted many years ago. The security warning I mentioned above is about a password that works on ALL units.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore