Posted: 2024-02-2810:22 AM. Last Modified: 2024-02-2811:21 AM
Configure HSTS Headers in NMC3
I am trying to configure HSTS headers for NMC3 network cards in UPS's and PDU's that we have, but have been unable to find the setting in the UI nor a command in the CLI to enable this. I have also been unable to find documentation on how to configure this. Does anyone know if this is possible? If so, could you share the command(s) to run or point me to some documentation I may have missed? Thanks!
EDIT: To anyone reading this in the future, this can be done in the command line with the command web -hs enable. It seems my firmware version is old and does not have this parameter for the web command. If you don't have this parameter either, try updating the firmware and see if you can do it then.