Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
Configure HSTS Headers in NMC3
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-02-2810:22 AM. Last Modified: 2024-02-2811:21 AM
Configure HSTS Headers in NMC3
I am trying to configure HSTS headers for NMC3 network cards in UPS's and PDU's that we have, but have been unable to find the setting in the UI nor a command in the CLI to enable this. I have also been unable to find documentation on how to configure this. Does anyone know if this is possible? If so, could you share the command(s) to run or point me to some documentation I may have missed? Thanks!
EDIT: To anyone reading this in the future, this can be done in the command line with the command web -hs enable. It seems my firmware version is old and does not have this parameter for the web command. If you don't have this parameter either, try updating the firmware and see if you can do it then.