I cannot get my SUA-1500 to communicate with my win7 ultimate 64bit system and can't figure out why. My serial ports check out fine using a loopback connector and other serial devices but I don't know how to veriify that the UPS serial port is working (USB works fine). I thought I might be able to verify proper communication if it were possible to connect to the UPS via PuTTY or Hyperterminal or similar terminal program. I am hoping that the UPS would be able to respond to a command or two (sorta like a modem AT command) which would demonstrate the I have a good "electrical" connection between the UPS and the PC...does anyone know if this is possible for test purposes and what a command/response might be?
I am using a 940-0024D serial cable and PowerChute v9 (didn't work with v8 either).
Any feedback would be much appreciated.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 11:20 PM . Last Modified: 2024-03-06 03:18 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 11:20 PM . Last Modified: 2024-03-06 03:18 AM
Thanks gentlemen...that worked fine. Now all I have to do is try to figure out why PowerChute is balking since I now "know" the hardware and connection is OK
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 11:20 PM . Last Modified: 2024-03-06 03:18 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 11:20 PM . Last Modified: 2024-03-06 03:18 AM
Thanks gentlemen...that worked fine. Now all I have to do is try to figure out why PowerChute is balking since I now "know" the hardware and connection is OK
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 11:20 PM . Last Modified: 2024-03-06 03:18 AM
Make sure that there is no application that is using the serial port. For testing you can use Putty and set the port settings to 2400-8-None-1-XOn/XOff. Once you are on the Putty screen press "Shift+Y", this should return an SM on the screen. Press "Shift+A" after seeing SM and this should produce a beep and the LEDs in front should flash once.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 11:20 PM . Last Modified: 2024-03-06 03:18 AM
i generally use no flow control and have have luck as well. may not hurt to try both settings.