Coldstart of an AP7922 PDU re-enables outlets that should be powered off.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Coldstart of an AP7922 PDU re-enables outlets that should be powered off.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

0 Likes
4
2205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

Coldstart of an AP7922 PDU re-enables outlets that should be powered off.

I had set an outlet on two AP7922 PDU's (firmware v3.7.3) to 'off' to prevent the attached device from powering up automatically during some electrical work in the server room. All power to the room was switched off, including both UPS's. When power was restored the PDU's cold started and all the outlets, including the one set to 'off' on both PDU's reverted to 'on' and provided power. This caused the attached device to boot which was not what I wanted.

I would have assumed that if an outlet on the PDU is set to 'off' it should remain off even when the PDU is cold booted. This does not appear to be the case. Can someone please confirm what the expected behaviour is?

Thanks,

Nigel.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

0 Likes
0
2204
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

OK, so I don't see any outlet delays set to never power on in there (under the [RackPDUOutlet] section) - had you changed the setting before posting the config?

Let me clarify what is normal and what is not normal. The PDU cannot save the current outlet state after a coldstart (power cycle) to the PDU. After a power cycle, the PDU should apply the coldstart delay (applies to the entire PDU) or the individual outlet power on delays (which one valid option is never meaning you'd have to manually control it to get it to come on).

For example, if you had a PDU outlet set to never turn on but had it currently turned on for whatever reason, if the PDU lost power and then was re-applied power, it'd follow the setting of never turned on and wouldn't remember that you specifically turned it on this one particular day and just reads the setting for the outlet upon that subsequent power up of the PDU.

Let me know if you have further questions.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

0 Likes
0
2205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

Can you provide me the event.txt and config.ini from this PDU to review before I comment? I forgot to add that I believe this is the way it works (the behavior you saw) but just wanted to verify.

Instructions here on downloading those -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

0 Likes
0
2205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

OK, so I don't see any outlet delays set to never power on in there (under the [RackPDUOutlet] section) - had you changed the setting before posting the config?

Let me clarify what is normal and what is not normal. The PDU cannot save the current outlet state after a coldstart (power cycle) to the PDU. After a power cycle, the PDU should apply the coldstart delay (applies to the entire PDU) or the individual outlet power on delays (which one valid option is never meaning you'd have to manually control it to get it to come on).

For example, if you had a PDU outlet set to never turn on but had it currently turned on for whatever reason, if the PDU lost power and then was re-applied power, it'd follow the setting of never turned on and wouldn't remember that you specifically turned it on this one particular day and just reads the setting for the outlet upon that subsequent power up of the PDU.

Let me know if you have further questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

0 Likes
0
2205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

Sorry, my misunderstanding. I set 1 outlet to 'off' under the Device Manager/Control/Outlet Control, thinking that it would remain in that state during a cold start of the PDU. From what you have said I should have configured the 'Power On Delay' to 'Never Power On' under Device Manager/Configuration/Outlet Configuration. This setting is preserved during a cold start?

Thanks,

Nigel.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

0 Likes
0
2205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:06 AM . Last Modified: ‎2024-03-18 12:07 AM

Correct smile

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore