Changing fans in the Symmetra SYMSTRF

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Changing fans in the Symmetra SYMSTRF
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:30 PM . Last Modified: ‎2024-03-14 04:26 AM

0 Likes
5
1386
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:30 PM . Last Modified: ‎2024-03-14 04:26 AM

Changing fans in the Symmetra SYMSTRF

The fans in our Symmetra are pretty loud... they are Nidec Alpha V T450. We are wondering if we can swap them with something quieter... I found some NMB fans that appear to be much quieter... however, I am concerned about the wiring. Can anyone help with the wiring? I see that the current "Nidec" fans we have installed have a 5-wire plug for each fan. Is it 3 phase + neutral and ground? How is it wired? The NMB fan appears to have a 2 pin connector... they are single phase. Here is the info on the NMB fans: http://www.nmbtc.com/pdf/acfans/4715ms.pdf The ones I have are: 4715MS-23T-B50-A00 - Also, I tried to get some Nidec quiet AC fans, but Nidec told me that the minimum quantity I can order is 75 fans!!! ha! - and nobody seems to be stocking them anywhere that I can tell... and on top of that, I still am unsure about the wiring. Here is the link to the quiet Nidec AC fans: http://catalog.nidec-servo.com/digital/english/general/g_fab/acsfan.html - I really wish APC offered a quiet fan "option" at least so I could just order plug-in replacements from APC that I knew would work well without all of this hassle...

Thanks,
Todd

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:30 PM . Last Modified: ‎2024-03-14 04:26 AM

0 Likes
0
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:30 PM . Last Modified: ‎2024-03-14 04:26 AM

No, unfortunately. I imagine it may be because of what they are located near.

Regardless, here are some details and instructions on that -> http://www.schneider-electric.us/support/index?page=content&country=US〈=en&locale=en_US&id=FA252227 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:30 PM . Last Modified: ‎2024-03-14 04:26 AM

0 Likes
0
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:30 PM . Last Modified: ‎2024-03-14 04:26 AM

Hi Toader,

The fans we use in Symmetra Power Array include a tachometer and presence sense line so that the Main Intelligence Module can report on their status. The 0M-606 Fan Assembly that is used in the Symmetra includes the Nidec fan with custom wiring to provide the tachometer functionality to the UPS.

I'm not aware of any off-the-shelf fans that will run in the Symmetra Power Array without modification to their wiring. If you were to find another fan with the same specification as the official 0M-606, you might be able to compare the wiring harness of the APC part to the alternate fan.

Please realize that we cannot comment on this matter any further, as using untested 3rd party components in the UPS is unsupported and not recommended. In the case of the fans, they are critical components which ensure the Isolation Transformers are able to operate within their specified thermal range. It's essential that the UPS is able to report to the user a legitimate fan failure, therefore we recommend the use of the official 0M-606 fan assembly in the Symmetra Power Array.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:30 PM . Last Modified: ‎2024-03-14 04:26 AM

0 Likes
0
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:30 PM . Last Modified: ‎2024-03-14 04:26 AM

I understand... and thank you for you answer. I am going to see if it is possible to rewire another fan. Also... I don't know if it would amount to anything, but is there anything you can do to urge APC to consider releasing a "kit" with quieter fans? Even according to my links above, Nidec Servo makes their AC silent fan series, so it seems unnecessary to use loud fans. I believe that there are LOTS and LOTS of customers out there would would consider swapping their fans for quieter ones... even on this forum alone, there are quite a few people talking about the noise. If there is anything APC can offer as a solution, that would be wonderful.

Thanks,
Todd

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:30 PM . Last Modified: ‎2024-03-14 04:26 AM

0 Likes
0
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:30 PM . Last Modified: ‎2024-03-14 04:26 AM

Hi Toader,

I can understand your request for a quiet fan kit from APC, but at this time the spare parts support plan for the discontinued Symmetra Power Array is to maintain availability of critical components. No new development or engineering effort is being spent on qualifying new parts such as quieter fans.

Our latest single-phase Symmetra offering, Symmetra LX, uses variable speed fans controlled by UPS logic. When your Symmetra Power Array was being developed in the mid-90s, the decision was made to use AC-powered constant velocity fans to ensure that the transformers are cooled even under worst-case load and environment conditions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:30 PM . Last Modified: ‎2024-03-14 04:26 AM

0 Likes
0
1383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:30 PM . Last Modified: ‎2024-03-14 04:26 AM

Are these fans hot swappable?Thanks!!

Tony

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:30 PM . Last Modified: ‎2024-03-14 04:26 AM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:30 PM . Last Modified: ‎2024-03-14 04:26 AM

No, unfortunately. I imagine it may be because of what they are located near.

Regardless, here are some details and instructions on that -> http://www.schneider-electric.us/support/index?page=content&country=US〈=en&locale=en_US&id=FA252227 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore